User: Dale001289, Location: Georgia
Asked on: Thursday, November 13, 2025 at 12:28 pm EST
Answered on: Thursday, November 13, 2025 at 12:28 pm EST
Question: We have delta-delta ungrounded MV power transformer, dry type, and the client wants to use fall of potential testing with a max ohms of 5 to earth. Is this test viable since there is no system grounded conductor?
You are correct to question the viability of Fall of Potential testing (FoP) on an ungrounded delta-delta transformer. Here's a breakdown of why it's problematic and what you can do instead
Why Fall of Potential (FoP) is Problematic on Ungrounded Systems:
FoP Test Principle
FoP testing relies on injecting a test current into the grounding electrode system (GES) and measuring the voltage drop created by that current as it returns to the source through the earth. The test measures the resistance of the earth around the grounding electrode. This resistance is an indicator of how well the grounding electrode system will dissipate fault current.
Ungrounded System's Lack of a Direct Return Path
An ungrounded delta-delta system intentionally does not have a direct, low-impedance return path for ground fault current. If a fault to ground occurs on one phase, the current path back to the source is through the stray capacitance of the system and the earth. This impedance is extremely high compared to a grounded system.
Minimal Test Current & Difficulty Measuring
Because there's no intentional return path, injecting a test current for FoP will result in:
Very low test current
The current will be limited by the high impedance of the earth.
Small voltage drop
The voltage drop measured between the auxiliary current electrode and the grounding electrode will be tiny and difficult to measure accurately.
Erratic readings
The readings will be highly susceptible to noise and stray currents in the earth, making them unreliable.
Meaningless Resistance Value
Even if you get a reading, the resistance value obtained from FoP is not directly indicative of the effectiveness of the grounding system in clearing faults. In an ungrounded system, the GES primarily serves to limit voltage during a fault, not to carry a large fault current back to the source. The 5 ohms target is not directly applicable.
In essence, the FoP test is designed for situations where you want to measure the effectiveness of the grounding electrode in providing a low-impedance path for fault current to return to the source. This is the opposite of what an ungrounded system is designed to do.What To Do Instead
Here's a more appropriate approach for verifying the safety and effectiveness of grounding in your ungrounded delta-delta system:1.
Grounding Electrode System (GES) Inspection and Testing
Visual Inspection
Thoroughly inspect the grounding electrodes, connections, and conductors for corrosion, damage, and proper installation. Verify the size and type of grounding conductors.
Ground Continuity Testing
Use a low-resistance ohmmeter (micro-ohmmeter) to verify the continuity and low resistance of the entire grounding electrode system. Test from the grounding electrode to all equipment grounding conductors (EGCs) connected to the transformer, enclosures, and other metal parts.
Ground Resistance Testing (Simplified)
While a traditional FoP test is not recommended for this system, measuring the resistance of the grounding electrode to a remote earth point can be beneficial. This test should be performed following ASTM G57/IEEE Standard 81. The purpose of this test is not to evaluate fault clearing performance, but to evaluate the grounding electrode resistance. The grounding electrode resistance is required by IEEE for limiting the maximum voltage potential rise for safety of personal in case of a ground fault.
2.
Insulation Resistance Testing (Megger Testing)
Phase-to-Phase and Phase-to-Ground
Perform insulation resistance tests on all transformer windings (primary and secondary) to ensure the insulation is in good condition. This helps prevent ground faults in the first place. This is a critical test for dry-type transformers.
Consider a Step Voltage Test
A step voltage test (applying increasing voltage levels) can provide more detailed information about the insulation condition than a single-voltage megger test.3.
Voltage Monitoring and Ground Fault Detection
Ground Fault Indication
Consider implementing a ground fault indication system. This typically involves voltage sensing devices that monitor the neutral-to-ground voltage. A significant voltage increase indicates a ground fault on one of the phases.
Transient Voltage Surge Suppression (TVSS)
Because ungrounded systems can experience transient overvoltages during a fault, installing TVSS (surge protection) can help protect equipment.4.
System Bonding and Grounding Practices
Equipment Grounding Conductors (EGCs)
Ensure that all metallic enclosures, equipment, and non-current-carrying parts of the electrical system are properly bonded together and connected to the grounding electrode system using EGCs.
Bonding Jumpers
Verify the presence and integrity of bonding jumpers around metallic conduits and other potential points of discontinuity in the grounding path.
In Summary
While you can try to perform FoP testing on the grounding electrode, the results may be difficult to obtain and hard to quantify for an ungrounded system. Focus on confirming proper grounding electrode system continuity, insulation testing of the transformer, and implementing a ground fault detection and surge protection strategy. This approach is more appropriate and effective for ensuring safety and reliability in an ungrounded delta-delta system. The aim is to:
Prevent Ground Faults
Focus on good insulation in the transformer.
Limit Voltage Rise During a Fault
Proper grounding and bonding will limit the potential rise on equipment enclosures during a ground fault.
Detect and Respond to Faults
A ground fault indication system will alert you to a problem.
Protect Against Transient Overvoltages: TVSS will help protect equipment from voltage spikes.Before performing any electrical testing, always consult with qualified electrical engineers and adhere to all applicable safety standards and regulations. Flag for review