Topic: Jockey pump tap terminals from ATS

User: hhsting, Location: Glen bunie, md, us

Asked on: Thursday, November 13, 2025 at 1:16 pm EST
Answered on: Thursday, November 13, 2025 at 1:16 pm EST

Question: I have listed fire pump controller, isolating switches and power transfer switch assembly. The load side terminal of the ATS also supplies Jockey Pump tap and fire pump.If the assembly is listed for fire pump can then ATS load side terminal also supply the jockey pump? Would that not invalidate the listing

You're asking a very important and nuanced question about fire pump system listings and their implications for connecting other loads. Here's a breakdown of the key considerations and how to interpret the listing requirements

Understanding Fire Pump System Listings (UL, FM, etc.)
Purpose of the Listing

Fire pump systems are listed as a complete integrated system to ensure reliable operation
solely for fire suppression. The listing focuses on the components working together to deliver water at the required pressure and flow rate during a fire emergency.

Scope of the Listing

The listing will explicitly define the components covered and the allowable configuration. This usually includes: Fire Pump Controller Fire Pump Motor Specific isolating switches (if included) ATS (if included as part of the fire pump system assembly) Interconnecting wiring within the listed assembly.

Listing Limitations

Critically, a listing for a fire pump assembly does not automatically allow adding other non-fire-related loads to the system. The listing is specific to the listed components operating together as designed.

The Jockey Pump Dilemma


The scenario you described is typical for fire pump applications; however, the code requires specific installation methods to follow. If it supplies the fire pump jockey then the following should be taken into account:1. Listing Restrictions

Most fire pump assembly listings do not include allowances for supplying a jockey pump from the ATS load side unless it's explicitly stated in the listing documentation. Adding the jockey pump could technically invalidate the listing if it modifies the tested and approved configuration.2.

NFPA 20 Requirements

NFPA 20 (Standard for the Installation of Stationary Fire Pumps) is the governing standard. NFPA 20 specifies the performance, testing, and reliability requirements for fire pump systems.

Exception to the Rule

NFPA 20 does allow for the jockey pump to be supplied from the fire pump power source,

BUT
it emphasizes reliability and segregation. NFPA 20 (2019) 10.8.
3.1 states: "A jockey pump shall be permitted to be supplied from the load side of the fire pump controller, provided that overcurrent protection is provided in accordance with 10.8.
3.2 and the jockey pump is not rated greater than 30 hp."3. Overcurrent Protection

NFPA 20 10.8.
3.2 states that "Overcurrent protection for the jockey pump shall be provided by fuses sized in accordance with NEC section 430.52 and 620.13". This is important because the overcurrent protection for the fire pump itself is intentionally sized very high (or omitted in some cases) to prevent nuisance tripping and ensure the pump runs until failure during a fire. The jockey pump needs proper overcurrent protection sized to its requirements so that it doesn't cause a failure of the entire system.


Reasons Why Adding Loads Can be Problematic for Listings
Load Calculations

The fire pump system listing is based on specific load calculations. Adding a jockey pump (or any other load) changes the total load on the ATS and potentially on the generator/utility feed. This could overload components or compromise the system's ability to start and run the fire pump under emergency conditions.


Coordination Issues

The overcurrent protection for the fire pump is specifically coordinated to allow the pump to run until failure (within reason). Adding another load could disrupt this coordination, potentially causing a protective device to trip and shut down the fire pump unnecessarily.

Harmonics and Voltage Drop

Additional loads, especially those with variable frequency drives (VFDs) or other nonlinear characteristics, can introduce harmonics and voltage drop into the system. This can affect the performance and reliability of the fire pump motor and controller.

What To Do
1. Consult the Listing

The most important step is to thoroughly review the listing documentation for the fire pump controller/system. Look for specific language addressing auxiliary loads, jockey pumps, or other connections. If it is not explicitly allowed, consider it not permitted under the listing.2.

Contact the Manufacturer

If the listing documentation is unclear or ambiguous, contact the manufacturer of the fire pump controller/system. They are the authority on the scope and limitations of their listing.3.

Separate Feeds

If the listing does
not allow for the jockey pump to be supplied from the ATS load side, then you must provide a separate, code-compliant power supply for the jockey pump. This could be from a normal power source with appropriate backup (e.g., generator).4.

Engineering Analysis

If you
must supply the jockey pump from the ATS load side and the manufacturer approves this and the listing does not prohibit it, have a qualified electrical engineer perform a detailed load calculation, coordination study, and voltage drop analysis. This will verify that the system can handle the additional load without compromising the fire pump's performance. This also confirms that the jockey pump has proper overcurrent protection without affecting the fire pumps operation.5.

AHJ Approval

Always consult with the local Authority Having Jurisdiction (AHJ). They have the final say in whether or not your installation meets the code and is acceptable. Be prepared to provide documentation, calculations, and manufacturer approvals.

In Summary


While NFPA 20 permits the jockey pump to be supplied from the fire pump power source under certain circumstances, you
cannot assume that a fire pump system listing automatically allows it.Careful review of the listing documentation, consultation with the manufacturer, and a thorough engineering analysis are essential to ensure code compliance and the reliability of the fire pump system.* If there's any doubt, providing a separate power supply for the jockey pump is the safest and most conservative approach. Flag for review