Question: 230.70 says the service disconnecting means shall be located "either outside of a building or structure or inside nearest the point of entrance of the service conductors." So this allows the unfused conductors to come out of the floor inside a building, going straight into a disconnect, a panel with a main, or switchgear. Does this mean a CT cabinet or feed-through meter cannot be in the building? With an indoor CT cabinet, the disconnecting means is not at the nearest point of entrance. Am I seeing this clearly?
You're seeing this generally correctly, and the interpretation of "nearest the point of entrance" is key and often debated. Let's break it down: The Rule
230.70 is very clear: Disconnecting means must be either outside or inside nearest the point of entrance. This is for safety – to allow firefighters or other emergency responders to quickly de-energize the building.
Unfused Conductors Inside
Yes, the NEC permits unfused service conductors to run inside the building to the disconnecting means, but only if that disconnect is "nearest the point of entrance." This is a critical limitation.
CT Cabinets and Feed-Through Meters Inside
This is where the ambiguity arises. You're correct that a CT cabinet before the disconnect complicates things. If the CT cabinet is located significantly further from the point of entry than the disconnecting means could be, then you likely violate 230.70.
"Nearest" is the Key Word
What constitutes "nearest" is not explicitly defined. It's a judgment call by the inspector, based on factors like:
Distance
How far is the CT cabinet from the entrance? Is it a few feet, or does it run across a significant portion of the building?
Accessibility
Is the disconnect readily accessible if located immediately inside the building, versus being further in after a CT cabinet?
Building Layout
The physical layout of the building will influence the determination of "nearest."
The Inspector's Call
Ultimately, the local electrical inspector has the final say. They will assess the specific installation and determine if the CT cabinet placement is in compliance.
Feed-Through Meters
Feed-through meters present the same issue. If the feed-through meter is inside the building, it has to be "nearest" the point of entrance.
How to Stay Compliant
Minimize Distance
If you must have a CT cabinet or feed-through meter inside, locate it as close as physically possible to the point of service entrance. Aim for the shortest run of unfused conductors inside the building.2.
Outdoor CT Cabinets/Meters
The simplest solution is often to locate the CT cabinet or meter outside the building. This eliminates the "nearest" debate. Many utilities prefer this anyway.3.
Integrated Equipment
Some manufacturers offer integrated service entrance equipment that combines the CTs, metering, and disconnecting means into a single, compact enclosure suitable for mounting at the point of entry.4.
Consult the Inspector
Always discuss the proposed service layout with the local electrical inspector before starting the installation. Get their feedback on the placement of the CT cabinet/meter relative to the disconnecting means. Document their opinion.5.
Consider an Exception (If Applicable)
Some jurisdictions or specific situations may have exceptions. Check with the local authority having jurisdiction (AHJ).
In summary: You've correctly identified the potential problem. While the NEC allows* unfused conductors inside, the "nearest the point of entrance" requirement is a significant restriction. A CT cabinet or feed-through meter inside the building can easily violate this requirement unless carefully positioned. It's critical to work closely with the electrical inspector to ensure compliance. Flag for review