Topic: Standby generator sizing with geothermal

User: fireryan, Location: Minnesota

Asked on: Thursday, November 13, 2025 at 6:55 pm EST
Answered on: Thursday, November 13, 2025 at 6:56 pm EST

Question: Im working on sizing a standby generator for a home with geothermal. The compressor unit or heat pump says is draws 44.8 amps at 240v. So that is 10,752 watts. The auxiliary heat in the unit is 9.6kw so total with them two alone is 20,352 watts. My question is when auxiliary heat kicks on in these geothermal units does the heat pump still run while the auxiliary heat is on or are they separate from one another? This will obviously affect my generator sizing significantly, never really dealt with geo thermal units so not sure how to size this

You're right to be careful with sizing the generator for a geothermal system, especially with auxiliary heat. Here's a breakdown of how these systems typically operate and how to approach sizing

How Geothermal Systems Operate with Auxiliary Heat
Geothermal as Primary Heating

Geothermal heat pumps are very efficient at extracting heat from the ground (or rejecting it into the ground for cooling). They work best when the temperature difference between the ground and the desired indoor temperature is relatively small.


Auxiliary Heat Kicks In

Auxiliary heat (electric resistance heat in your case) comes into play when:

Extreme Cold

When the outside temperature is very low (or very high in cooling mode), the geothermal heat pump's capacity might not be enough to meet the heating load.


Defrost Cycle

During very cold weather, the outdoor coil on an air-source heat pump (which acts as the indoor coil during heating in a geothermal system) can ice up. The system will reverse to run in cooling mode for a short period to defrost the coil. Auxiliary heat is often engaged during the defrost cycle to prevent a blast of cold air.

Emergency Heat

If the geothermal compressor fails, the auxiliary heat can be used as a backup to provide heat.


Rapid Temperature Recovery

After a setback period (e.g., nighttime temperature turned down), the homeowner might want to quickly raise the temperature. Auxiliary heat can supplement the heat pump to speed up the process.

Heat Pump and Auxiliary Heat - Simultaneous Operation



In most cases, the heat pump
will continue to run when auxiliary heat is active.
The auxiliary heat is there to supplement the heat pump, not replace it. This is the key to understanding the load.

Sizing the Generator

Here's the recommended approach:1. Calculate Starting Watts and Running Watts for the Heat Pump



Running Watts

You've already calculated this: 44.8 amps 240 volts = 10,752 watts.

Starting Watts

Heat pumps, especially those with scroll compressors, have a significant inrush current (starting watts). You need to find this information.

Crucially, check the compressor manufacturer's data sheet or the unit's nameplate.
Look for LRA (Locked Rotor Amps). A common rule of thumb is to multiply the running amps by 3 to estimate starting watts, but LRA is more accurate if available.Example: If LRA = 150 amps, then starting watts = 150 amps 240 volts = 36,000 watts. Important Note

Some modern heat pumps have "soft start" technology to reduce the inrush current. If the unit has soft start, the starting watts will be much closer to the running watts. Verify if your unit has this feature.2.

Calculate Running Watts for Auxiliary Heat

You already have this: 9.6 kW = 9600 watts.
3.


Calculate Total Running Watts with Auxiliary Heat Active

Total = Heat Pump Running Watts + Auxiliary Heat Watts Total = 10,752 watts + 9600 watts = 20,352 watts4.

Calculate Total Starting Watts

The highest of the starting watts for either the heat pump or the auxiliary heat will be the peak you need to cover. Electric resistance heat (auxiliary heat) does not have inrush current issues like a motor does, so it is the heat pump you need to focus on. Total Starting Watts = Heat Pump Starting Watts (e.g., 36,000 watts from the example above).5.

Add Other Essential Loads

Lights, refrigerator, well pump (if applicable), furnace fan (if separate), essential circuits, etc. Get accurate wattage information for these. For motors (like the well pump), you'll need to estimate starting watts (often 3x running watts).6.

Consider a Safety Factor

Add at least 10-20% safety factor to your total calculated watts. This accounts for inaccuracies in estimates and future load additions.7.

Choose the Generator

The generator should have a continuous (running) wattage rating higher than your calculated total running watts. The generator should have a surge (starting) wattage rating higher than your calculated total starting watts.

Example Scenario


Let's say:
Heat Pump Running Watts: 10,752 watts Heat Pump Starting Watts: 36,000 watts (based on LRA) Auxiliary Heat Watts: 9,600 watts Other Essential Loads: 3,000 watts (running), 9,000 watts (surge - includes well pump starting) Total Running Watts: 10,752 + 9,600 + 3,000 = 23,352 watts Total Starting Watts: MAX(36,000, 9,000) = 36,000 watts With a 10% Safety Factor: Running Watts: 23,352 1.10 = 25,687 watts Starting Watts: 36,000 1.10 = 39,600 watts You would need a generator with at least 26 kW continuous and 40 kW surge capacity.Important Considerations and Tips Nameplate Data is King

Always rely on the equipment's nameplate data for accurate amperage and wattage ratings.

Professional Load Calculation

For critical applications, it's best to have a qualified electrician or HVAC technician perform a professional load calculation.


Load Management

Consider load shedding devices. These can automatically disconnect non-essential loads when the generator is near capacity, preventing overload.

Fuel Type

Consider the availability and cost of different fuel types (propane, natural gas, diesel).


Automatic Transfer Switch (ATS)

An ATS is essential for automatically switching the home's power source between the utility grid and the generator during an outage.*

Maintenance:
Regular generator maintenance is crucial for reliable operation.By carefully calculating the loads and considering the operational characteristics of the geothermal system, you can select the appropriate generator size to provide reliable backup power. Good luck! Flag for review