Topic: Transfer Switch

User: kcunningham59, Location: Audubon, NJ

Asked on: Thursday, November 13, 2025 at 11:43 pm EST
Answered on: Thursday, November 13, 2025 at 11:44 pm EST

Question: I had a 1200A Asco Transfer Switch with 8 conduits coming in from the 2 sources. I need to go back out with 4 sets of conduits underground again to the final destination. That’s a lot of conduits in and out of this switch. Would you guys come out the side into a pull box and then go underground? Into LB’s the down? Looking for thoughts here.

Okay, this is a common and challenging situation. Let's break down the options and considerations for routing conduits in and out of your 1200A ASCO transfer switch.

Understanding the Problem

You have: Source Side

8 conduits entering the transfer switch.


Load Side

4 conduits exiting to underground.

Physical Constraint

Many conduits concentrated at the transfer switch location. This leads to bending radii issues, conduit fill issues, and physical congestion.

Options and Considerations


Here's a breakdown of options, with pros and cons, and what I'd lean towards based on your description

1. Direct Entry/Exit with LB's:

Description

Continue to use LB fittings directly at the transfer switch enclosure to transition to underground.

Pros

Simplest in theory. Potentially avoids the cost of an additional pull box.

Cons



Extremely Congested

12 conduits terminated directly at the transfer switch enclosure will be a nightmare to pull, maintain, and troubleshoot. Bending radii inside the enclosure will be very tight. Difficult and time consuming to make terminations.


Potential Code Violations

Exceeding bending radius requirements inside the enclosure. Insufficient working space.

Difficult to Work On

Future maintenance and modifications will be a nightmare.


Not Recommended for Conductor Size

I am assuming you are running larger conductors for a 1200A ATS, using LB's and pulling through those will cause jacket damage and pull tension issues.

2. Side Exit to Pull Box, then Underground



Description

Exit the transfer switch horizontally into a pull box mounted adjacent to the switch. Then, transition down to underground from the pull box.


Pros



Decouples Conduit Congestion

Moves the tight bending and conduit routing
away from the transfer switch enclosure.

Easier Pulling

A larger pull box provides space for easier conductor pulling and reduced bending stress.

Future Flexibility

Easier to add or modify conduits later.


Better Access

Easier to access connections in the pull box for maintenance.

Reduces Stress on Transfer Switch Enclosure

The transfer switch enclosure won't be subjected to the weight and stress of multiple conduits directly attached.


Cons

Cost of the pull box. Requires space for the pull box. Requires additional conduit runs from the transfer switch to the pull box.

3. Variations on the Pull Box Approach



Trough/Gutter Instead of Box

A continuous wireway (trough or gutter) could be used instead of a pull box. This provides more linear space for routing and potentially simpler pulls. You'd still transition down to underground from the wireway.

Vertical Pull Box

A tall, narrow pull box (oriented vertically) could be used if horizontal space is limited. This allows you to route conduits in from the transfer switch and then bend down inside the box for the underground exit.

Recommendation and Considerations
I strongly recommend option #2: Using a pull box (or wireway) adjacent to the transfer switch.

Here's why:
Long-Term Value

It's worth the extra cost and effort upfront to create a system that is maintainable, expandable, and code-compliant. A congested conduit system is a problem waiting to happen.

Safety

Easier pulls reduce the risk of conductor damage and potential electrical hazards.


Practicality

In the real world, electrical work often requires modifications or additions. A pull box makes these changes much easier and safer.

Conductor Size

With a 1200A system, you're dealing with large conductors. Pulling these through numerous tight bends within the transfer switch enclosure will be extremely difficult and could damage the insulation.

Detailed Considerations for the Pull Box Approach


Pull Box Sizing (NEC 314.28)

This is crucial! NEC 314.28 specifies the minimum size of pull boxes and junction boxes based on the size of the conduits entering and exiting, as well as the number of conductors.
Consult the NEC for the exact formulas. Undersized pull boxes are a common and costly mistake.* Pay special attention to the rules for angle pulls and straight pulls. With 8 entries and 4 exits, you'll need to ensure the pull box is sized appropriately. It will likely need to be relatively large. Consider using a custom-sized box if necessary.2.

Conduit Type

Specify appropriate conduit type for underground use (e.g., PVC-coated rigid, RMC with proper corrosion protection).3.

Sealing

Ensure that all underground conduits are properly sealed to prevent water ingress.4.

Grounding

Bond the pull box to the grounding system.5.

Support

Properly support the pull box and all conduits.6.

Pulling Compound

Use approved pulling lubricant to reduce friction during conductor installation.7.

Conductor Bending Radius (NEC 312.6)

Ensure that the conductor bending radius inside the transfer switch enclosure and the pull box meets or exceeds code requirements.8.

Accessibility

Ensure that the pull box has adequate working space around it for future maintenance.9.

Conduit Fill (NEC Chapter 9)

Double-check that your conduit fill calculations are correct.10.

LB's

If space is limited and you must use an LB, use the largest sweep possible and consider using a conduit body with a removable cover for easier access.

Steps to Take


Detailed Conduit Layout

Create a detailed conduit layout plan. This should show the exact routing of all conduits, the location of the pull box, and the dimensions of the pull box.2.

Pull Box Sizing Calculation

Perform a thorough pull box sizing calculation based on NEC 314.28.
3.


Material List

Develop a complete material list, including conduits, fittings, pull box, grounding hardware, sealing compound, and pulling lubricant.4.

Electrical Inspection

Obtain the necessary electrical permits and schedule inspections.5.

Qualified Contractor

Use a qualified and experienced electrical contractor to perform the installation. The contractor should be familiar with the NEC and local electrical codes.

In Summary


While the pull box option adds cost and complexity, it is the best long-term solution for managing conduit congestion and ensuring a safe, reliable, and maintainable electrical system. Prioritize proper planning, code compliance, and the use of a qualified contractor. Flag for review