Mike Dolt Enterprises Logo Mike Dolt Enterprises

Topic: Transfer Switch Conduit Routing

User: kcunningham59, Location: Audubon, NJ

Asked on: Thursday, November 13, 2025 at 11:51 pm EST
Answered on: Thursday, November 13, 2025 at 11:51 pm EST

Question: I had a 1200A Asco Transfer Switch with 8 conduits coming in from the 2 sources. I need to go back out with 4 sets of conduits underground again to the final destination. That’s a lot of conduits in and out of this switch. Would you guys come out the side into a pull box and then go underground? Into LB’s the down? Looking for thoughts here.

Okay, you've got a tricky situation with a high-amp transfer switch and a bunch of conduits. Here's a breakdown of considerations and potential solutions, leaning towards the pull box approach for manageability

Understanding the Problem:
Congestion

Stuffing that many conduits directly into and out of the transfer switch enclosure is going to be a nightmare. Tight bends, difficulty pulling conductors, and general maintenance headaches will be constant.


Bending Radius

Large conductors (especially at 1200A) have minimum bending radius requirements. Trying to make those bends inside or immediately exiting the transfer switch enclosure will be difficult, and potentially violate code.

Heat Dissipation

A large number of conduits packed together, especially those with high current-carrying conductors, can trap heat. While the underground portion will help with heat dissipation, the area around the switch could become a concern.


Code Compliance (NEC)

You need to be mindful of: Conduit fill limitations (how much of the conduit cross-sectional area can be occupied by conductors). Bending radius requirements for conductors. Working space requirements around electrical equipment. Protection of conductors from physical damage (underground burial depth, etc.).

Why a Pull Box is Likely the Best Approach



Decoupling and Organization

The pull box acts as a transition point. You can make neater, more manageable connections
within the pull box. This makes pulling wires easier and significantly simplifies future maintenance or modifications.

Easing Bends

The pull box allows you to make gradual, code-compliant bends on the large conductors. You're not forced to cram everything into the confined space of the transfer switch enclosure.

Accessibility

A properly sized pull box provides much better access for pulling, splicing (if necessary), and inspecting conductors.


Separation

You can use the pull box to physically separate the incoming and outgoing conduits, which can help with organization and cable identification.

Flexibility

Using a pull box gives you flexibility in terms of conduit routing and orientation.

Detailed Breakdown of Options & Considerations


Pull Box (Recommended)



Location

Mount the pull box directly adjacent to the side of the transfer switch enclosure. This minimizes the length of the conductors needed to transition from the switch to the box.

Size

CRITICAL. The pull box must be sized according to NEC 314.28, which dictates minimum dimensions based on the size of the largest raceway entering the box and the number of conductors being pulled through.

This needs to be calculated carefully by a qualified electrician or engineer.
Don't underestimate the size needed. Err on the side of larger. You can have one large junction box serve both sides of the ATS or you can utilize two separate pull boxes. Construction

Use a NEMA 3R (or higher, depending on the environment) rated pull box. It needs to be weatherproof. Consider a steel or aluminum box, depending on your grounding requirements and corrosion concerns. Stainless steel might be appropriate in harsh environments.

Conduit Connections

Use appropriate conduit fittings (e.g., rigid metal conduit connectors or compression connectors) to connect the conduits to the pull box. Ensure a watertight seal, especially for underground runs.


Grounding

Ground the pull box properly. The NEC has specific requirements for grounding conductor enclosures, particularly in high-current systems.

Conductor Supports

Within the pull box, provide adequate support for the conductors to prevent strain on the terminations at the transfer switch and at the conduits exiting the box. Use cable cleats, cable ties, or other appropriate methods.


Labeling

Clearly label all conductors and conduits within the pull box. This is essential for future troubleshooting.2.

LB Fittings (Less Desirable, Potentially Problematic)



Not Recommended for This Scale

While LBs
can be used, they are generally not appropriate for this situation. The large number of conductors and the need for large bending radii make it extremely difficult to use LBs effectively.

Bending Radius Issues

It would be nearly impossible to maintain proper bending radius for 1200A conductors exiting an LB fitting and immediately turning downward. You'd likely violate code.

Limited Access

LBs provide very limited access for pulling and terminating conductors, and for future maintenance.


Conduit Fill Issues

You may struggle to get all the conductors to fit into the available space within the LB fitting and conduit run.3.

Direct Connection (Almost Certainly Impractical)



Extremely Difficult

Directly connecting all those conduits to the transfer switch enclosure would be a physical impossibility.


Code Violations

Bending radius, conduit fill, and working space requirements would almost certainly be violated.

Maintenance Nightmare

Any future maintenance or modifications would be extremely difficult and time-consuming.

Step-by-Step Implementation (Pull Box Method)


Planning and Design



Consult with a qualified electrician or electrical engineer.
This is essential. They can perform the necessary calculations, select the proper equipment, and ensure code compliance. Determine pull box size. Use NEC 314.28. Plan conduit routing. Consider burial depths, underground obstructions, and the location of other utilities. Select appropriate conduits and fittings. RMC (Rigid Metal Conduit) is often a good choice for underground applications, but other options may be suitable depending on the environment. Develop detailed drawings. Show conduit runs, pull box locations, and conductor routing.2. Installation



Install the pull box.
Mount it securely to a concrete pad or other suitable support. Run conduits. Install the conduits according to your plan. Ensure proper burial depths and support. Pull Conductors

This is where the pull box
really pays off. You can pull the conductors in manageable sections.

Terminate Conductors

Make secure terminations at the transfer switch and within the pull box. Use appropriately sized connectors.

Grounding

Ground the system according to NEC requirements.


Labeling

Clearly label all conductors and conduits.

Important Considerations



Conductor Type and Size

The conductors must be rated for the 1200A load and the environmental conditions. Consider insulation type (e.g., THHN/THWN, XHHW).


Overcurrent Protection

Ensure that the overcurrent protection (fuses or circuit breakers) is properly sized to protect the conductors.

Coordination Study

If this is a critical system, a coordination study should be performed to ensure that the overcurrent protection devices will operate properly in the event of a fault.


Local Codes and Regulations

Check with your local building department for any specific requirements that may apply.*

Qualified Personnel

This work should only be performed by qualified electricians who are familiar with high-current electrical systems and the NEC.

In summary, using a pull box is the most practical and code-compliant way to handle the transition from the transfer switch to the underground conduits. It provides the necessary space for bending conductors, facilitates pulling and terminating wires, and simplifies future maintenance. But, get a qualified electrician or electrical engineer involved from the start to ensure that the system is designed and installed correctly.
Flag for review

Previous Question Next Question