Question: I had a 1200A Asco Transfer Switch with 8 conduits coming in from the 2 sources. I need to go back out with 4 sets of conduits underground again to the final destination. That’s a lot of conduits in and out of this switch. Would you guys come out the side into a pull box and then go underground? Into LB’s the down?
Okay, you've got a congested situation at your transfer switch! Managing that many large conduits is a common challenge. Here's a breakdown of factors to consider and a discussion of your suggestion (and other possible solutions)
Understanding the Problem
Physical Space
The primary issue is the physical congestion around the transfer switch. Cramming that many conduits in and out directly is difficult for installation, maintenance, and future modifications.
Bending Radius
Large conduits, especially with larger conductors, have minimum bending radius requirements. Trying to make sharp turns directly at the switch could violate code and damage conductors.
Pulling Effort
Pulling conductors through multiple bends (especially 90-degree LB fittings) significantly increases pulling tension. Exceeding the allowable pulling tension can damage conductors.
Accessibility
Future access for troubleshooting, maintenance, and conductor replacement is essential. A dense cluster of conduits makes this difficult.
Code Compliance
You must adhere to the NEC (National Electrical Code) or your local electrical code, which covers conduit fill, bending radii, support requirements, and working clearances.
Evaluating Your "Pull Box" Suggestion
Your idea of transitioning to a pull box is a good starting point. Let's break it down: Pros
Decoupling
The pull box decouples the tight conduit layout at the transfer switch from the underground run. This simplifies the immediate connections to the switch.
Space Management
The pull box provides more space to manage the conductors as they transition from the 8 incoming conduits to the 4 outgoing conduits. You can make larger, code-compliant bends within the box.
Easier Pulling
You can perform conductor pulls in shorter segments. You can pull the conductors from the source equipment to the Pull Box, then pull from the Pull Box to the transfer switch. This can significantly reduce pulling tension.
Accessibility
The pull box provides a point of access for future conductor inspections, testing, and potential replacements.
Cons
Cost
Pull boxes and their associated installation add to the overall project cost.
Space Requirement
The pull box itself requires physical space, which might be a constraint.
Water Intrusion
Underground pull boxes are susceptible to water intrusion. Proper sealing and drainage are critical.
LB Fittings Directly into the Ground Pros
Simplicity
The design seems simple.
Cons
Accessibility
Makes pulling and future maintenance very difficult.
Conductor Damage
The number of bends increase the possibility of conductor damage.
Alternative Solutions & Considerations1. Sizing the Pull Box
NEC Requirements
NEC Article 314 covers pull boxes, junction boxes, and handhole enclosures. It specifies minimum dimensions based on the size and number of conductors entering and exiting the box. You must calculate the minimum pull box size according to the code.
Straight Pulls
For straight pulls, the length of the box must be at least eight times the trade diameter of the largest raceway.
Angle or U Pulls
For angle or U pulls, the distance from each raceway entry to the opposite wall of the box must be at least six times the trade diameter of the largest raceway, plus the sum of the diameters of all other raceways on the same wall and row. This is a more complex calculation.
Depth and Width
You also need adequate depth and width to properly arrange the conductors within the box.
Oversizing
It's generally a good idea to slightly oversize the pull box to provide more working space and accommodate future changes.2.
Conduit Material and Installation
RMC (Rigid Metal Conduit)
Offers the best physical protection for underground runs.
IMC (Intermediate Metal Conduit)
A lighter-weight alternative to RMC, offering good protection.
PVC (Polyvinyl Chloride Conduit)
A cost-effective option, but requires more care in installation to prevent damage and requires proper burial depth for physical protection.
Expansion Fittings
If using PVC conduit, use expansion fittings to accommodate thermal expansion and contraction.
Sealing
Properly seal all conduit connections and the pull box to prevent water intrusion.3.
Conductor Selection and Pulling
Conductor Type
Use conductors rated for wet locations (e.g., THWN-2, XHHW-2).
Conductor Size
Verify conductor ampacity based on the load and NEC requirements.
Pulling Compound
Use a listed pulling compound to reduce friction during conductor installation.*
Pulling Equipment
Use appropriate pulling equipment to avoid exceeding conductor pulling tension limits. Consider using a dynamometer to monitor pulling force.4.
Consider "Ganged" Multiple Smaller Transfer Switches
Depending on the load, instead of a single 1200A switch, look into a design with multiple smaller paralleled transfer switches. This can reduce the conduit size significantly.
Recommendations1. Detailed Load Calculation
Review the load calculations to confirm the 1200A service is correct. Optimize conduit fill with paralleled conductors if necessary to minimize conduit size.2.
Consult with an Electrical Engineer
Given the complexity of the situation, it's highly recommended to consult with a licensed electrical engineer experienced in power distribution systems. They can perform the necessary calculations, develop a detailed design, and ensure code compliance.3.
Select a High-Quality Pull Box
Choose a pull box rated for underground use with a watertight cover. Consider materials like fiberglass or polymer concrete, which are resistant to corrosion.4.
Plan the Conduit Layout Carefully
Develop a detailed conduit layout, considering bending radii, support requirements, and accessibility.5.
Pulling Calculations
Perform pulling calculations to estimate pulling tension and select appropriate pulling equipment.
In summary, using a pull box to transition between the transfer switch and the underground conduits is a viable solution, but it needs to be carefully planned and executed. Consulting with an electrical engineer is highly recommended to ensure a safe, reliable, and code-compliant installation. Flag for review