Topic: Aluminum EMT: ground bushings

User: barryohm, Location: California

Asked on: Friday, November 14, 2025 at 4:37 am EST
Answered on: Friday, November 14, 2025 at 4:41 am EST

Question: We are Installing Aluminum EMT.Not much in the code yet? Seems there is more to come like distance of Supports? Places allowed to use? Are ground bushings required e? Any thoughts?

You're right, Aluminum EMT is relatively new compared to steel EMT (Electrical Metallic Tubing), so the code coverage is still evolving. Let's break down your questions and some important considerations

Code Coverage and Future Changes
Limited Initial Coverage

You'll find the basic requirements for EMT applicable to aluminum EMT as well, such as article 358 which may cover usage, installation, and bending.


Growing Recognition

As aluminum EMT gains wider acceptance, the NEC (National Electrical Code) will likely incorporate more specific provisions. Keep an eye on future editions of the NEC for these additions.

Specific Questions and Considerations
1. Distance of Supports



Generally Same as Steel EMT (Initially)

For now, you'll typically need to follow the support requirements for steel EMT. This means:


10-foot Spacing

Maximum spacing between supports for straight runs.

3 feet

Within 3 feet of boxes, conduit bodies, or other termination points.


Code Variations

Some local codes might have more stringent requirements. Always check with your local electrical inspector.

Potential for Change

There
is the potential for different support distances in the future if research indicates aluminum EMT behaves differently structurally under load or temperature changes. It's good to stay updated.2.

Places Allowed to Use



Similar to Steel EMT

Aluminum EMT generally shares the same acceptable locations as steel EMT. These usually include:

Exposed and Concealed

Both indoors and outdoors.


Dry, Damp, and Wet Locations

Appropriate fittings rated for the environment are crucial.

Corrosion Concerns

Aluminum is naturally corrosion-resistant but can react with certain materials (e.g., direct contact with dissimilar metals in wet environments). Use compatible fittings and avoid direct contact with concrete or other materials that can cause corrosion.


Specific Restrictions

Be aware that certain occupancies (e.g., healthcare facilities) or specific types of equipment may have restrictions on the use of aluminum conduit due to grounding and safety concerns.

Check Listing and Manufacturer's Instructions

Always check the product listing and the manufacturer's instructions for any specific limitations on use.3.

Are Ground Bushings Required?
Depends on the Installation

Ground bushings (or grounding wedges) are required when:

Conduit Size

The NEC typically requires grounding bushings on metallic conduits (including aluminum) 1 inch or larger. This is to ensure a low-impedance ground fault path.


Knockout Size

When using concentric or eccentric knockouts that reduce the cross-sectional area of the grounding path.

Bonding Jumpers

In some cases, you might need bonding jumpers in addition to ground bushings to ensure adequate grounding continuity.


Proper Installation is Key

Simply using a ground bushing isn't enough. It must be properly installed and connected to the grounding electrode system.

Aluminum-Specific Fittings

Use ground bushings and bonding jumpers specifically designed for aluminum to prevent galvanic corrosion at the connection points.

General Thoughts and Best Practices
Consult with Local Authorities

The most important step is to consult with your local electrical inspector or Authority Having Jurisdiction (AHJ). They have the final say on what's acceptable in your area.

Stay Updated on Code Changes

Subscribe to industry publications, attend training seminars, and regularly review the latest NEC editions to stay informed about changes related to aluminum EMT.


Proper Installation

Aluminum EMT requires proper installation techniques. Use tools designed for aluminum conduit, avoid over-tightening fittings, and protect the conduit from physical damage.

Consider Corrosion

Take steps to prevent corrosion, especially in damp or wet environments. Use compatible fittings, apply corrosion-inhibiting compounds, and avoid direct contact with dissimilar metals.


Manufacturer's Instructions

Always follow the manufacturer's instructions for installation and use.*

Proper Grounding

Ensure the entire system is properly grounded according to the NEC and local codes. This is critical for safety.

In summary,
aluminum EMT offers advantages like lighter weight and corrosion resistance. However, its code coverage is still developing. For now, follow the requirements for steel EMT where applicable, pay close attention to grounding, and always consult with your local electrical inspector. Stay informed about future code changes. Flag for review