Question: We are Installing Aluminum EMT.Not much in the code yet? Seems there is more to come like distance of Supports? Places allowed to use? Are ground bushings required e? Any thoughts?
You're right, Aluminum EMT is relatively new compared to steel EMT (Electrical Metallic Tubing), so the code coverage is still evolving. Let's break down your questions and some important considerations
Code Coverage and Future Changes
Limited Initial Coverage
You'll find the basic requirements for EMT applicable to aluminum EMT as well, such as article 358 which may cover usage, installation, and bending.
Growing Recognition
As aluminum EMT gains wider acceptance, the NEC (National Electrical Code) will likely incorporate more specific provisions. Keep an eye on future editions of the NEC for these additions.
Specific Questions and Considerations1. Distance of Supports
Generally Same as Steel EMT (Initially)
For now, you'll typically need to follow the support requirements for steel EMT. This means:
10-foot Spacing
Maximum spacing between supports for straight runs.
3 feet
Within 3 feet of boxes, conduit bodies, or other termination points.
Code Variations
Some local codes might have more stringent requirements. Always check with your local electrical inspector.
Potential for Change
There is the potential for different support distances in the future if research indicates aluminum EMT behaves differently structurally under load or temperature changes. It's good to stay updated.2.
Places Allowed to Use
Similar to Steel EMT
Aluminum EMT generally shares the same acceptable locations as steel EMT. These usually include:
Exposed and Concealed
Both indoors and outdoors.
Dry, Damp, and Wet Locations
Appropriate fittings rated for the environment are crucial.
Corrosion Concerns
Aluminum is naturally corrosion-resistant but can react with certain materials (e.g., direct contact with dissimilar metals in wet environments). Use compatible fittings and avoid direct contact with concrete or other materials that can cause corrosion.
Specific Restrictions
Be aware that certain occupancies (e.g., healthcare facilities) or specific types of equipment may have restrictions on the use of aluminum conduit due to grounding and safety concerns.
Check Listing and Manufacturer's Instructions
Always check the product listing and the manufacturer's instructions for any specific limitations on use.3.
Are Ground Bushings Required? Depends on the Installation
Ground bushings (or grounding wedges) are required when:
Conduit Size
The NEC typically requires grounding bushings on metallic conduits (including aluminum) 1 inch or larger. This is to ensure a low-impedance ground fault path.
Knockout Size
When using concentric or eccentric knockouts that reduce the cross-sectional area of the grounding path.
Bonding Jumpers
In some cases, you might need bonding jumpers in addition to ground bushings to ensure adequate grounding continuity.
Proper Installation is Key
Simply using a ground bushing isn't enough. It must be properly installed and connected to the grounding electrode system.
Aluminum-Specific Fittings
Use ground bushings and bonding jumpers specifically designed for aluminum to prevent galvanic corrosion at the connection points.
General Thoughts and Best Practices Consult with Local Authorities
The most important step is to consult with your local electrical inspector or Authority Having Jurisdiction (AHJ). They have the final say on what's acceptable in your area.
Stay Updated on Code Changes
Subscribe to industry publications, attend training seminars, and regularly review the latest NEC editions to stay informed about changes related to aluminum EMT.
Proper Installation
Aluminum EMT requires proper installation techniques. Use tools designed for aluminum conduit, avoid over-tightening fittings, and protect the conduit from physical damage.
Consider Corrosion
Take steps to prevent corrosion, especially in damp or wet environments. Use compatible fittings, apply corrosion-inhibiting compounds, and avoid direct contact with dissimilar metals.
Manufacturer's Instructions
Always follow the manufacturer's instructions for installation and use.*
Proper Grounding
Ensure the entire system is properly grounded according to the NEC and local codes. This is critical for safety.
In summary, aluminum EMT offers advantages like lighter weight and corrosion resistance. However, its code coverage is still developing. For now, follow the requirements for steel EMT where applicable, pay close attention to grounding, and always consult with your local electrical inspector. Stay informed about future code changes. Flag for review