Question: My question:As per IEC 60076-1 is allowed uk% tolerances (positives and negatives).For short circuit issues is possible to request to manufacturers that NEGATIVE TOLERANCES are not allowed? Or even BOTH TOLERANCES?
Yes, as per IEC 60076-1, the standard specifies tolerances on the declared value of the short-circuit impedance voltage (Uk%). These tolerances are usually both positive and negative.Now, to answer your core question
Yes, it is possible to request manufacturers not to allow negative tolerances (or even both tolerances) on Uk%
.Here's a breakdown of why and how: IEC 60076-1 as a Baseline, Not a Limit
IEC 60076-1 provides minimum requirements and guidelines. It doesn't preclude you from specifying stricter or different requirements in your technical specification or purchase order. It's a standard framework.
Custom Specification is Allowed
Your technical specification is a contractual document that overrides certain aspects of the standard. If your engineering analysis determines that a negative tolerance on Uk% creates unacceptable risks related to short-circuit stress on upstream equipment, you have every right to specify "Uk% tolerance: +X%, -0% (or +0%)" or "Uk% tolerance: +X%, +Y%".
Reasoning for Restricting Tolerances (Short-Circuit Perspective)
Negative Tolerance Risks
A lower-than-expected Uk% means a higher short-circuit current. This higher current puts greater stress on upstream circuit breakers, cables, and other components in your electrical network. It also leads to higher mechanical forces on the transformer windings during a fault. You want to ensure that your upstream protection devices can interrupt the maximum possible fault current.
Both Tolerances (Strict Control)
In some exceptionally critical applications, you might even specify a very tight positive tolerance range (+X% to +Y%). This would happen if your network requires a very precise level of fault current limitation, and even small variations in Uk% could affect the coordination of protective devices.
Manufacturer Considerations
Be prepared for a few potential implications when you impose tighter tolerance requirements:
Cost
Tighter tolerances often increase manufacturing complexity and require more stringent testing and quality control. Expect to pay more.
Lead Time
Meeting tighter tolerances may extend the manufacturing lead time.
Feasibility
Extremely tight tolerances might be technically challenging or even impossible for certain transformer designs or power ratings. Discuss the feasibility with the manufacturer before finalizing the specification.
How to Request Specific Tolerances
Clearly State the Requirement
In your technical specification for the transformer, explicitly state the required Uk% tolerance. For example: "The short-circuit impedance voltage (Uk%) shall be [Declared Value] ± X%, -0%." "The short-circuit impedance voltage (Uk%) shall be [Declared Value] + X%, + Y%." (or simply say: Uk% shall be between [min value] and [max value]) "Negative tolerances on Uk% are NOT permitted."2.
Justification (Optional but Recommended)
Briefly explain why you are imposing the tighter tolerance. This helps the manufacturer understand the importance of the requirement and ensure they can meet it. For example, "This requirement is necessary to ensure adequate short-circuit protection of upstream equipment and maintain system stability."3.
Manufacturer Consultation
Engage with the manufacturer early in the specification process. Discuss the feasibility of your requirements, potential cost implications, and testing methods. This collaborative approach will help you get the best possible outcome.
In summary: You absolutely can request manufacturers to limit or eliminate negative tolerances (or impose very tight tolerances overall) on the short-circuit impedance voltage (Uk%) of a transformer. Ensure your technical specification clearly states your requirements and engage in discussions with the manufacturer to ensure feasibility and cost-effectiveness. Your decision should be based on a thorough evaluation of your electrical network's short-circuit duty and the impact of Uk% variations. Flag for review