Topic: Drilling holes in Conduit Bodies

User: jes25, Location: Midwest

Asked on: Friday, November 14, 2025 at 1:19 pm EST
Answered on: Friday, November 14, 2025 at 1:19 pm EST

Question: All the other threads on supporting conduit bodies beg the question, can we drill a hole in one to support it?I think yes. I don't think conduit bodies even need to be listed so I don't see a problem there.

Okay, let's break this down. You're asking a very specific and practical question about the legality and safety of drilling a hole in a conduit body for support. Here's my assessment

Arguments for NOT Drilling Conduit Bodies (Generally the Prevailing View)
Intended Use and Listing

While you are right that not every conduit body
must be listed (especially smaller ones), the intent is that they are used as a junction or pulling point in a conduit system. The UL listing (or equivalent) would only cover the product as it's designed and tested to be used, the product would no longer be UL listed if you alter it.

Compromising Integrity

Drilling a hole can compromise the structural integrity of the conduit body, especially if the hole is too large, poorly placed, or if the body is made of a thinner material (like aluminum). This weakens its ability to protect the conductors inside. Think about vibration, physical impacts, and the weight of the connected conduit runs.

Corrosion

Drilling a hole exposes the bare metal (unless you meticulously treat the edge) and creates a point where corrosion can start, particularly in damp or corrosive environments.

Code Compliance

The NEC (National Electrical Code) generally requires that electrical equipment be installed according to its listing and labeling (NEC 110.3(B)). Altering a listed product can violate this requirement. Furthermore, specific articles dealing with conduit often refer back to proper support methods.


Available Alternatives

There are many readily available, code-compliant ways to support conduit bodies:

Straps

Conduit straps designed for the conduit size and type.


Clamps

Conduit clamps for rigid, EMT, or IMC.

Hangers

Various hanger types specifically for conduit.


Strut Systems

Unistrut or similar systems provide flexible support options.

Supporting the Conduit Run

Frequently, supporting the conduit run itself adequately supports the attached conduit bodies.

Arguments for
POTENTIALLY Drilling Conduit Bodies (Under Very Specific Circumstances, and Still Risky)



Small Hole, Careful Placement

If the hole is very small (think pilot hole size), precisely placed away from stress points (corners, threaded areas), and the conduit body is made of a robust material (like thick-walled steel), and you address corrosion protection after drilling, the structural impact might be negligible.

Non-Critical Application

In a situation where the conduit body is in a protected environment, subject to minimal stress, and failure would not create a significant hazard, you might be able to justify it to yourself. However, that doesn't make it code-compliant or necessarily safe.



AHJ Approval

The
only way to be sure is to get explicit permission from the Authority Having Jurisdiction (AHJ). Present them with your specific situation, the conduit body type, the hole size and location, and your rationale. Be prepared for them to say no.

Why You're Likely to Get Pushback

Even if you
think it's okay, most electricians and inspectors will strongly advise against it for the reasons listed above. It's generally perceived as a shortcut and a potential compromise to safety and code compliance.

Bottom Line

While it's
possible to argue that under extremely specific and controlled circumstances, drilling a small hole in a conduit body might not be catastrophic, it's generally a bad idea. It's almost certainly a code violation without specific AHJ approval, and it's generally considered unprofessional. There are almost always better, code-compliant, and safer ways to support conduit bodies.

Recommendations


Use appropriate straps, clamps, or hangers designed for conduit support.2.

Support the conduit run itself.3.

If you have a truly unique situation, consult with the AHJ
before doing anything.4.

Document everything carefully if you do get permission.
*In short, don't drill the conduit body. Use the right hardware for the job. It's safer, easier, and more likely to pass inspection. Flag for review