Asked on: Friday, November 14, 2025 at 5:48 pm EST
Answered on: Friday, November 14, 2025 at 5:48 pm EST

Question: I am tasked with the design of a 300-400 amp service for a 6000 ft new build. The power pole with the transformer and the meter is 150 feet away. I don't know a plausible installation with a disconnect at the outside of the house or at the power pole. Two 200-amp feeds keep entering my mind, but I think it has to be a 300-400 disconnect.

Okay, let's break down the options and considerations for a 300-400 amp service to your 6000 sq ft new build with a 150-foot run from the power pole. A 300-400 amp service is substantial, so let's approach this systematically

Key Considerations:

1. Load Calculation

This is absolutely critical. Before deciding on 300A, 320A, or 400A, you must perform a thorough load calculation according to the National Electrical Code (NEC). This will factor in square footage, appliances, heating/cooling, lighting, electric vehicle charging (if anticipated), and any other significant electrical loads. Don't guess. Underestimating can lead to overload, fire hazards, and code violations. Overestimating is expensive.2.

NEC Requirements

The NEC dictates how service entrances must be installed, including wire sizing, grounding, disconnect locations, and overcurrent protection. You must adhere to these requirements.3.

Local Codes and Utility Regulations

Your local building codes and the utility company's rules will often have specific requirements that may go beyond the NEC. Contact the local building department and the utility company early in the process. They will likely have requirements for meter base placement, types of service entrance conductors allowed, grounding requirements, and disconnect locations.4.

Voltage Drop

At 150 feet, voltage drop becomes a very real concern, especially under heavy load. You'll need to calculate voltage drop for each conductor size you're considering. The NEC recommends limiting voltage drop to 3% for branch circuits and 5% overall. Exceeding this can cause appliance malfunction, overheating, and decreased efficiency.5.

Cost

Larger conductors and higher-rated equipment are more expensive. Balance performance and code compliance with your budget.6.

Future Expansion

Consider whether you might need to add significant electrical loads in the future (e.g., a workshop, a pool, another EV charger). It's often cheaper to upsize the service now than to upgrade it later.7.

Accessibility

The disconnect must be readily accessible.8.

Working Space

Clear working space is required around the disconnect to be code compliant.

Plausible Installation Options (assuming the load calculation justifies 300-400 amps)



Option 1: Single 300-400 Amp Service with Disconnect at the House
Description

A single set of large service entrance conductors runs from the meter at the pole to a 300-400 amp service disconnect at the house.

Pros

Simpler wiring inside the house (one main panel). Potentially lower cost than two separate services.


Cons



Voltage Drop

This is the biggest challenge. You'll need very large conductors to minimize voltage drop. Consider parallel runs.


Conductor Size and Cost

Large conductors are expensive and difficult to work with.

Trenching and Conduit

Requires a trench and conduit (PVC or rigid metal) buried to the proper depth (as dictated by local code). Check for any restrictions on the type of conduit allowed.


Disconnect Placement

You need a suitable, accessible location for the disconnect at the house.

Wiring

To handle the load, and to address voltage drop you may need to run 4/0 aluminum or 250kcmil copper in parallel.


Important Considerations



Parallel Runs

If conductor sizes become impractical, you might consider running conductors in parallel. This means two or more sets of conductors connected to the same terminals at both ends. The NEC has specific rules for paralleling conductors (see NEC 310.10(H)).


Aluminum vs. Copper

Aluminum is less expensive than copper for the same ampacity. However, it requires careful installation (proper torque on connections and the use of anti-oxidant compounds) to prevent corrosion. Copper is generally preferred for its lower resistance and easier installation, but the cost can be a significant factor.

Option 2: Single 300-400 Amp Service with Disconnect at the Pole
Description

The service disconnect is located at the power pole, right after the meter. A feeder then runs from the disconnect to a distribution panel inside the house.

Pros

Could be easier to manage the heavy conductors close to the pole. Potentially cheaper than running very large service entrance conductors all the way to the house.


Cons



Disconnect at the Pole

Requires an enclosure at the pole that is weatherproof and lockable. Must be easily accessible.


Feeder to House

The feeder from the pole to the house must still be sized to handle the full load and minimize voltage drop.

Grounding

Proper grounding at both the pole and the house is critical.


Coordination with Utility

The utility company may have specific requirements or restrictions on the placement and type of disconnect at the pole.

Wiring

The feeder from the disconnect at the pole to the house needs to be sized appropriately based on the load calculation and voltage drop considerations.


Important Considerations



Utility Approval

Getting the utility's approval for a disconnect at the pole is crucial.


Option 3: Two 200-Amp Services (Less Recommended)
Description

Two separate 200-amp services are run from the pole to the house, each with its own meter and disconnect.


Pros

Potentially easier to work with smaller conductors. May be easier to distribute the load.

Cons



More Expensive

Two meter bases, two disconnects, and potentially higher utility connection fees.

Complex Wiring

Requires careful balancing of the load between the two panels.


Aesthetics

Two meter bases may not be aesthetically pleasing.

Rarely Approved

Most utility companies will not approve multiple services for a single-family dwelling. It is usually only for multi-family dwellings or outbuildings.


Why it's less recommended

The increased cost and complexity usually outweigh any potential benefits.

Steps to Take


Accurate Load Calculation

Hire a qualified electrician or engineer to perform a thorough load calculation for the entire house. This is the foundation for everything else.2.

Contact the Utility Company

Discuss your plans with the utility company. They will tell you their requirements for service entrance conductors, metering, disconnects, and grounding. Get it in writing!3.

Contact the Local Building Department

Check for any local code requirements that may be more stringent than the NEC.4.

Consult with a Licensed Electrician

Work with a licensed electrician to design the service entrance, select the appropriate conductors and equipment, and ensure that the installation complies with all applicable codes and regulations. Get multiple bids.5.

Consider an Engineer

For services of this size, it is worth considering hiring an engineer to design the electrical service.6.

Prepare a Detailed Plan

Develop a detailed plan that includes a wiring diagram, conduit layout, grounding details, and equipment specifications.7.

Obtain Permits

Obtain all necessary permits before starting any work.8.

Professional Installation

Have a licensed electrician perform the installation.

Important Notes



Safety First

Working with electricity is dangerous. Always de-energize circuits before working on them. If you are not comfortable working with electricity, hire a qualified electrician.


Grounding is Critical

Proper grounding is essential for safety and to prevent electrical problems. The grounding system must be installed according to the NEC and local codes.*

Conduit Fill

Ensure that the conduit is not overfilled with conductors. The NEC specifies maximum conduit fill percentages.

In summary, the best option is likely a single 300-400 amp service with the disconnect either at the house or the pole, depending on the utility's preferences and the specific site conditions. The key is to minimize voltage drop by using appropriately sized conductors and careful installation practices. Avoid two separate services unless there are very specific reasons to justify it. The only way to know for sure is to get a load calculation, speak with the utility, and get quotes from qualified electricians.