Question: Has anyone ever installed split duct fiberglass conduit? Obviously it goes around existing cables. It's attched with H-strip and zip ties.I'm trying to labor the conduit in my database and there are not NECA labor units but I'm think the labor should be slightly higher than the same NON SPLIT conduit. Thoughts?

You're right to consider the labor impact of split duct fiberglass conduit. It's not a common material with standardized labor units, so you'll need to estimate. Here's a breakdown of why it takes more time and how to factor that into your labor estimation

Why Split Duct Takes More Labor Than Solid Duct:
Handling

Even though it's lightweight, handling the two halves of the conduit and ensuring they align properly around existing cables adds time.


Alignment & Fitting

Aligning the two halves and ensuring they seat correctly, especially around bends or existing supports, takes more finesse than simply pushing a solid conduit into place.

H-Strip Application

Cutting, applying, and securing the H-strips requires careful measurement and application.


Zip Tie Placement & Tightening

Strategic placement and tightening of zip ties to maintain a secure enclosure add to the installation time.

Obstacles

Working around existing cables can be difficult.


Potential for Cutting

Depending on the situation cutting might be required.

Inspection

More attention to detail is needed to ensure a secure and complete enclosure.

Estimating Labor Impact

Here's a practical approach to factoring in the additional labor:1.

Base Comparison

Start with the labor units for the same size of rigid non-split fiberglass conduit. This gives you a baseline for the raw conduit run.2.

Markup Factor

Apply a percentage markup to that baseline to account for the additional work. The percentage will vary based on conditions (access, height, complexity of the run).


Easy Conditions (straight runs, easy access, minimal obstructions)

Add 20-30%

Moderate Conditions (some bends, average access, some obstructions)

Add 30-40%


Difficult Conditions (complex runs, poor access, many obstructions)

Add 40-50% or higher.

Example

Let's say you have a straight 20-foot run of 4" split fiberglass duct in "Moderate" conditions. NECA (or your database) shows 1 hour per 10 feet for 4" rigid fiberglass conduit. Base Labor for 20 feet: 2 hours Markup Factor: 35% (for moderate conditions) Additional Labor: 2 hours 0.35 = 0.7 hours Total Estimated Labor: 2 hours + 0.7 hours = 2.7 hours

Considerations for Your Database



Notes Field

In your database,
clearly note that you've used a modified labor unit for split conduit. Document the base labor unit and the percentage markup applied. This helps with future estimates and provides transparency.

Material Item Description

Include "SPLIT" in the material description. This makes it clear to anyone reviewing the estimate what type of conduit is being used.

Track Actuals

After the job is complete, track the actual labor hours spent installing the split duct. Compare it to your estimate. This data will help you refine your markup factors for future projects.


Crew Experience

Crew experience is a factor. An experienced crew will have a smaller markup than a less experienced crew.

In Summary:


While there are no standardized labor units, by comparing to similar conduit types and applying a reasonable markup based on the complexity of the installation, you can create a defensible and accurate labor estimate for split duct fiberglass conduit. Remember to document your assumptions and track actuals for continuous improvement. Flag for review