Question: In 220.61(B)(1) and in other parts of 220 it says you can have a service supplying household cooking units, but that’s not listed in 230.2 as an acceptable use of a service. Where does it permit this?

You've hit upon a valid point and potential source of confusion when reading the NEC. You're right, 230.2 specifically addresses when a building or other structure can be supplied by a single service (or more than one). Household cooking appliances aren't explicitly listed there.However, the key is to understand the scope of 230.2 and how it relates to load calculations like those found in Article 220.Here's the breakdown:1. 230.2 is about number and type of services, not about allowable loads. 230.2 primarily dictates the circumstances under which you're allowed to have more than one service feeding a building, or to have specific types of services (e.g., fire pump services). It addresses the physical entry point of power and the basic configuration of the service, not what the power is used for after it enters the building.2. Article 220 deals with load calculations. Article 220 provides the rules for calculating the electrical demand of a building or portion thereof. It tells you how to figure out how much power you need to supply. Sections like 220.61(B)(1) provide specific demand factors you can use for calculating the service load for household cooking appliances. It assumes that a service is already permitted and is addressing how to calculate the load it will be required to support.3. The allowance for household cooking appliances is implied by the very existence of Article 220's rules. If the NEC didn't allow a service to supply household cooking appliances, it wouldn't provide rules for calculating the load of those appliances. The presence of these rules implies that such a service is permitted under the broader framework of the NEC.4. Household cooking appliances are typical loads. Almost all residential and many commercial buildings will have cooking appliances. Buildings served under Article 230 are permitted to supply any and all of the loads calculated under Article 220.

Example to Illustrate

Imagine a single-family dwelling.

230.2(A) would say
: "One building or other structure shall be supplied by only one service." (with certain exceptions). This means you generally can't have two separate services feeding the same house without a specific reason outlined in 230.2. Article 220 would say: "Okay, now that you have this one service, let's figure out how big it needs to be. You have lighting, receptacles, a water heater, and cooking appliances. Let's use 220.55 to apply demand factors to the cooking appliances to determine their contribution to the overall service load."In short: 230.2 doesn't explicitly say "you can have a service supplying cooking appliances." However, Article 220's sections on load calculation for cooking appliances implicitly allow it, as the NEC wouldn't provide rules for calculating the load of something that wasn't permitted. The main point is that 230.2 is about the architecture of the service, while Article 220 is about the size* of the service needed for its intended loads.Therefore, you don't need an explicit statement in 230.2 that cooking appliances are allowed. The fact that Article 220 provides rules for calculating the load for these appliances is sufficient to imply that they are permissible loads on a service, subject to the overall requirements of the NEC. Flag for review

Previous Question Next Question