Mike Dolt Enterprises Logo Mike Dolt Enterprises

Topic: 3-Hour Firewall Penetration for SER

User: codycl, Location: DFW

Asked on: Tuesday, November 18, 2025 at 9:36 am EST
Answered on: Tuesday, November 18, 2025 at 9:48 am EST

Question: Hey guys!In my 18 years in the trade, I have yet to need to come to a forum to ask for help, but the time has come.We are building a multifamily project with two sub-levels of garage with 5-stories of wood structure above. Basically, the two main electrical rooms that feed everything are in the basement below Level 1. I have chase/leave-out locations in the Level 1 slab above these two main electrical rooms with the plans of running SER from the equipment, through the leave-outs in the slab, then through the 5-story wood-framed structure to feed house panels and meter centers throughout.My issue is that there is a 3-hour firewall separating one of the sections. I have approval from the city to penetrate the firewall with electrical cable, as long as we use the correct fire device/assembly/method. Most of the SER will be 250 KCM 3-Phase Aluminum. I am familiar with 2-hour penetrations in walls and floors, but I reached out to our firestopping rep, and he said it would be "an engineering decision" regarding the 3-hour penetration.This is beyond anything I'm capable of figuring out on my own at this time, I dont understand the UL systems, etc, so if you can help me, I'll do my best to help you with a little consultation reward, haha. I'm desperate at this point.Thank you in advance

Alright, this is a tricky one, but definitely solvable. Here's a breakdown of what you need to do and how to approach it, along with explanations to help you understand the UL systems. I'll try to give you practical steps you can take right now.

Understanding the Problem Fire Rating

A 3-hour firewall means the barrier must resist fire for a minimum of 3 hours, preventing the spread of flames and smoke. Penetrations significantly weaken this resistance.


SER Cable

The SER cable itself isn't fire-rated. It will burn and melt, creating a hole through the firewall.

UL Systems

UL (Underwriters Laboratories) develops and tests firestop systems to determine their fire resistance. Each system is assigned a UL number, which documents the specific materials, installation methods, and fire-resistance rating achieved during testing.


Engineering Judgement

Your firestopping rep is right. A 3-hour fire rating for electrical penetrations, especially with larger conductors like 250 kcmil, often pushes beyond standard, readily available tested solutions. That's where engineering judgment comes in. It's not that it can't be done, it's that it likely requires a custom-engineered solution.

Steps to Take Now (Practical & Urgent)
1. Re-Engage Your Firestopping Rep, But More Precisely



Be specific

Tell them exactly the type and size of cable you are using: 250 kcmil Aluminum SER cable, number of conductors, and cable diameter.


Reiterate the 3-hour requirement.
Ask for their recommendations for firestop manufacturers that have engineers on staff who can assist with developing a custom engineered solution. They know the manufacturers best and which ones are most responsive. Emphasize your need for documentation that will satisfy the AHJ (Authority Having Jurisdiction)

You need a letter or report from the firestop manufacturer stating that their proposed system meets or exceeds the 3-hour rating and is suitable for your specific application.

Don't be afraid to push back

If they can't provide specific recommendations, ask who they would recommend you contact directly for engineering support. You are paying for their expertise, make them earn it.2.

Contact Firestop Manufacturers Directly



Hold off on contacting the Firestop Manufacturer
until you speak to the firestopping rep. The rep will be able to steer you in the right direction. If they cannot, call the main number of the top Firestop manufacturers. Be prepared with all the information

Cable type, size, number of conductors, penetration size, type of wall/floor (concrete, drywall, etc.), and specific firewall rating.


Ask for their engineering department directly.
Explain that you need assistance specifying a 3-hour firestop system for electrical cable penetrations. Ask for Case Studies or Past Approvals

Inquire if they have dealt with similar situations. They might have a previously engineered solution that can be adapted.3.

Consider a Fire-Rated Shaft Enclosure (Possible Alternative - Requires Design Review)

Instead of individually firestopping each cable penetration, consider encasing all the cables in a fire-rated shaft enclosure as they pass through the firewall and extend upwards. This would create a protected pathway. This will likely require coordination with the architect and structural engineer. The shaft itself would need to be built with materials that meet the 3-hour fire-resistance rating. This may only be a viable solution if the penetration through the firewall is not yet complete, or is fairly large.4.

Document Everything!
Keep meticulous records of all your conversations, emails, and recommendations from firestopping reps and manufacturers. This documentation is crucial for the AHJ.

Common Firestopping Products/Techniques (FYI)



Firestop Putty

Often used for small penetrations (e.g., small wires). Not typically suitable for large cable bundles.

Firestop Sealant

Applied around penetrations to prevent the passage of flame and smoke. Requires proper depth and backing materials.


Firestop Pillows

Bags filled with fire-resistant material that expand when exposed to heat. Useful for larger openings and cable trays.

Firestop Collars

Intumescent collars that are wrapped around combustible pipes and cables. They expand when heated, crushing the burning material and sealing the penetration.


Mineral Wool

Used as a packing material in larger openings, combined with firestop sealant.

Understanding UL Systems (Simplified)


UL systems are categorized by: Penetration Type

What is penetrating the barrier (e.g., electrical cables, pipes, ducts).


Construction Type

The material and thickness of the wall or floor (e.g., concrete, drywall, wood).

Fire Rating

The fire resistance rating (e.g., 1-hour, 2-hour, 3-hour).


Specific Materials and Installation

The exact firestopping products and installation methods used during testing.When you find a UL system that seems close, always verify that it matches your specific conditions. Small variations can invalidate the rating.

Example of a Possible Approach (Highly Dependent on Specific Products and Approvals)



Concrete Slab Penetration

You might need to core a slightly larger opening than the cable bundle requires.


Packing

Pack the annular space (the gap between the cables and the concrete) tightly with a fire-rated mineral wool packing material.

Firestop Compound

Apply a thick layer of a UL-listed firestop sealant on both sides of the penetration, embedding the cable bundle and mineral wool. The specific sealant and application depth will depend on the UL listing you find.


Firestop Collar

Using a Firestop Collar on each individual cable might be a solution if you have room.

Important Considerations



AHJ Approval

The Authority Having Jurisdiction (e.g., building inspector) has the final say. Get their input early in the process. Show them the UL systems you're considering and any engineering documentation you obtain.


Installation Quality

Proper installation is critical. Follow the manufacturer's instructions meticulously. Consider having a certified firestop installer perform the work.

Future Changes

If cables are added or removed in the future, the firestop system
must* be re-evaluated and re-sealed.

The "Consultation Reward"


Don't worry about a consultation reward just yet. Focus on getting this solved. If you're still stuck after trying these steps, and if I can provide further specific guidance based on the manufacturer feedback you receive, then we can talk. Good luck! Let me know how it goes. Flag for review

Previous Question Next Question