Mike Dolt Enterprises Logo Mike Dolt Enterprises

Topic: Wire Size

User: Alwayslearningelec, Location: NJ

Asked on: Tuesday, November 18, 2025 at 10:45 am EST
Answered on: Tuesday, November 18, 2025 at 10:45 am EST

Question: As an example circuit #11 HWP-104. the FLA is 77 amps but the fuse is 150A. So the OCPD(150a Fuse) wire needs to be sized to at least 150A? I am a little confused because the FLA is 77A. I guess your also need to add 125% to the 77A?

Okay, let's break down how to properly size the wire for a circuit with a motor load, considering the information you've provided and relevant electrical codes.

Understanding the Terms



FLA (Full Load Amps)

This is the current a motor draws when operating at its rated voltage and horsepower. 77A is the motor's FLA in your example.


OCPD (Overcurrent Protective Device)

This is the fuse or circuit breaker that protects the circuit from overloads and short circuits. In your example, it's a 150A fuse.

Ampacity

This is the current-carrying capacity of a conductor (wire) under specific conditions without exceeding its temperature rating.

Key Principles and Code Requirements (Primarily based on the NEC - National Electrical Code in the US, but the general principles apply internationally)


Motor Branch Circuit Conductor Sizing

The general rule is that motor branch circuit conductors must have an ampacity of
at least 125% of the motor's FLA.2.

Motor OCPD Sizing

The OCPD (fuse or circuit breaker) protects the motor and the conductors. Motor OCPD sizing can be a bit more complex, depending on the motor type and starting method. The NEC allows for larger OCPDs for motors than would be allowed for continuous lighting or receptacle loads to allow for motor inrush current (the high current drawn when a motor starts). This is why the 150A fuse is larger than the 77A FLA.

Calculations and Steps


Conductor Ampacity Calculation

Calculate 125% of the FLA: 77A 1.25 = 96.25A The wire must be sized to carry at least 96.25 amps.
2.


Wire Sizing based on Ampacity

Consult an ampacity table (NEC Table 310.16 or similar) to determine the appropriate wire size for an ampacity of 96.25A. The wire size depends on the insulation type (e.g., THHN, THW) and the ambient temperature. For example, using NEC Table 310.16 for copper conductors with THHN insulation, assuming an ambient temperature of 30°C (86°F), you would need at least a #3 AWG copper conductor (which has an ampacity of 100A). A #4 AWG wire has a rating of only 85A and is not adequate for this application.
3.


OCPD (Fuse) Sizing Considerations

You've stated the OCPD is 150A. The NEC has specific rules regarding the maximum allowed size of the OCPD for motor circuits, as it's meant to protect the motor from overloads but also allow it to start. The specific rules for OCPD sizing depend on the motor's design letter (NEMA Design A, B, C, or D), starting method, and whether it's a single-phase or three-phase motor. For a typical motor (Design B), the NEC generally allows a fuse to be sized up to 175% of the motor's FLA. For an inverse time breaker, you could be as high as 250%. However, always consult the NEC and specific manufacturer data for your particular motor.

In this case, 175% of 77A = 134.75A. A 150A fuse might be permissible if it's necessary to allow the motor to start without nuisance tripping and if it's allowed by the NEC and other applicable standards, and the manufacturer's specifications. However, remember that exceeding the maximum allowed OCPD size can create a safety hazard. The 150A OCPD is rated above the ampacity of the wire so the wire must be sized to the OCPD and not the 77a FLA.


Important Considerations and Cautions



NEC (or your local electrical code)

Always consult the latest edition of the NEC (or your local electrical code) for the specific requirements in your jurisdiction. Electrical codes are safety standards and are legally binding.

Motor Nameplate

Refer to the motor's nameplate for the exact FLA, service factor, and other relevant information. The nameplate information is crucial for proper circuit design.


Ambient Temperature

Wire ampacity is affected by ambient temperature. If the conductors are in a hot environment, you may need to use a larger wire size to compensate for the temperature derating. Consult the ampacity tables and derating factors in the NEC.

Voltage Drop

Consider voltage drop, especially for long circuit runs. Excessive voltage drop can cause the motor to overheat and operate inefficiently. Use a larger wire size if necessary to keep voltage drop within acceptable limits.


Qualified Electrician

This information is for educational purposes only. Electrical work can be dangerous. Always consult a qualified and licensed electrician for the design and installation of electrical circuits.

Manufacturer's Instructions

Always follow the motor manufacturer's recommendations for wiring and overcurrent protection.

In Summary:
1. Calculate the minimum conductor ampacity (125% of FLA).
2. Select a wire size with an ampacity equal to or greater than the calculated value, considering insulation type, ambient temperature, and voltage drop.3. Verify that the OCPD size is appropriate for the motor, based on the NEC and the motor manufacturer's recommendations. A larger OCPD than the conductor ampacity is allowed for motor starting, but it must be within the code limits and it determines the minimum required wire size.
4. In your example, the 150A fuse likely dictates the minimum wire size. You
must* use a wire with an ampacity of at least 150A because the OCPD is that size.By following these steps and adhering to the NEC and other applicable standards, you can ensure a safe and reliable motor circuit. Remember to consult a qualified electrician for any electrical work. Flag for review

Previous Question Next Question