Mike Dolt Enterprises Logo Mike Dolt Enterprises

Topic: Clearance

User: Maravilla24, Location: Maryland

Asked on: Tuesday, November 18, 2025 at 1:03 pm EST
Answered on: Tuesday, November 18, 2025 at 1:04 pm EST

Question: I have a riser room where I have bus plugs. On the South side of the room, I have 1'9" and I was wondering if we really need 2' there to walk around it? Is it required by code? Unfortunately, I can't move the equipment North because there are existing structural beams on the way in the floor.Please advice.

You're asking about working clearance requirements for electrical equipment, specifically around bus plugs in a riser room. Here's a breakdown of the relevant considerations and what the code says

Understanding the Code (Primarily Based on the NEC - National Electrical Code):
NEC 110.26(A) - Spaces About Electrical Equipment

This is the key section in the NEC that dictates working space around electrical equipment operating at 600 volts, nominal, or less to ground. It's all about safety for personnel who need to inspect, maintain, and operate the equipment.


Key Factors Determining Clearance

The required clearance depends on several factors:

Voltage to Ground

This is the voltage between any live part of the busbar and ground (typically the enclosure). Since you're talking about bus plugs, it's highly probable that it's 480V or 208V systems.


Condition 1, 2, or 3

This refers to the conditions on the opposite side of the working space:

Condition 1

Exposed live parts on one side and grounded parts (like a concrete wall, grounded metal enclosure, etc.) on the other side.


Condition 2

Exposed live parts on one side and insulated parts on the other side.

Condition 3

Exposed live parts on both sides.


Table 110.26(A)(1)

This is the table in the NEC that provides the minimum working clearance distances based on the voltage to ground and the Condition (1, 2, or 3).

Applying the Code to Your Situation


Determine Voltage to Ground

You need to know the voltage from any live part of the busbar to ground. This is critical. Common voltages are 208V, 480V, or 600V.2.

Determine the Condition

Carefully consider what's on the opposite side of the 1'9" space. Is it a grounded wall, another piece of electrical equipment (live parts?), or something else? If the South side of your riser room is a grounded wall (like a concrete wall), it's likely

Condition 1
. If there's another piece of electrical equipment on the South side with exposed live parts, it's Condition 3. If it's an insulated surface with no exposed live parts, it is likely Condition 2.3. Consult Table 110.26(A)(1)

Once you know the voltage to ground and the Condition, you can find the
minimum required clearance in the table.

Example

Let's say your bus plugs are on a 480V system and you have a grounded wall (Condition 1). Table 110.26(A)(1) requires a minimum working clearance of 3 feet.4.

Height and Width

Besides depth, the NEC also requires:

Height (110.26(A)(3))

The working space must be clear and extend from the grade, floor, or platform for the height specified in 110.26(E) (typically 6'6" or the height of the equipment, whichever is greater).


Width (110.26(A)(2))

The width of the working space must be the width of the equipment or 30 inches, whichever is greater.

Addressing Your 1'9" (21 Inches) Situation



Highly Unlikely to be Code Compliant

Given that you're dealing with bus plugs, it's almost certain that the voltage to ground will require more than 21 inches of working clearance. The code is quite firm on these requirements.


The Exception for "Dead-Front" Equipment is Unlikely to Apply

There's a limited exception that might apply if the equipment is "dead-front" (meaning there are no exposed live parts on the front). However, bus plugs, by their very nature of being designed for quick connection, rarely qualify for that exception.

Why is this clearance so important?
Safety

The clearance is there to allow a qualified electrician to safely work on the equipment without accidentally coming into contact with live parts. It also gives them room to maneuver and use tools.


Access

It provides enough room to access the equipment for maintenance, repairs, and inspections.

Possible Solutions & Recommendations


Re-evaluate Condition

Double-check the South side of the room. Is it absolutely a grounded surface? If so, you're dealing with Condition 1.2.

Seek an Exception (Highly Unlikely)

You could try to get an exception from the Authority Having Jurisdiction (AHJ) (usually the local building or electrical inspector). However, they are very unlikely to grant an exception to working clearance requirements due to the safety implications.3.

Move the Equipment (If Possible)

You said you can't move it North due to structural beams. Can you move it East or West instead? This might involve rerouting some of the bus duct.4.

Modify the Room (Expensive)

Can you expand the riser room southward? This is likely the most expensive option.5.

Downstream Protection

Provide an appropriately sized overcurrent protective device feeding the bus plugs, so they can be de-energized and worked on safely.6.

Consult with a Qualified Electrical Engineer

This is strongly recommended. They can properly assess the situation, perform calculations, review the code requirements, and propose the best solution for your specific circumstances. They can also work with the AHJ to ensure compliance.

In summary, 1'9" is almost certainly insufficient working clearance for bus plugs. Consult a qualified electrical engineer immediately to determine the correct clearance requirements and find a code-compliant solution. Safety is paramount!
Flag for review

Previous Question Next Question