User: Therealcrt, Location: Kansas City

Asked on: Tuesday, November 18, 2025 at 2:53 pm EST
Answered on: Tuesday, November 18, 2025 at 2:58 pm EST

Question: Building an 3 phase 4 wire 208/120v 800a overhead service. Per plans is exactly what I’m doing. Next to the 800a disconnect is a 400a meter enclosure and next to that is a 400a disconnect that will feed a 2 section 400a panel inside. From the 800a disconnect to the meter I’m running parallel 250AL. As well to the 400a disco from the meter. So now my question. I know the 400a needs a EGC from the 800a service disconnect soAm I allowed to use the meter can as a “pass through” for the grounds to travel from 800a to 400a? As the meter can does not need an EGC. I will put a bonding locknut from the nipple between 800a and meter to bond the meter can. And also my power company requires the meter can to have a GEC ran to it as well not just at the 800a service disconnect. So I will bond that to the neutral inside the meter can. Thanks !

Okay, let's break this down and address your questions about the grounding and bonding of your 208/120V, 800A service. Your understanding is generally good, but let's clarify some points.

Understanding the NEC Requirements Service Equipment

The 800A disconnect is your service equipment. Everything downstream from it is considered a feeder.


Equipment Grounding Conductor (EGC)

An EGC must be run with the feeder conductors to the 400A disconnect to provide a low-impedance path back to the source (the 800A service disconnect) for fault current. This is crucial for safety.

Bonding

Bonding is connecting all metal parts to create a path for fault current to travel. This helps trip overcurrent devices.


Grounding Electrode Conductor (GEC)

The GEC connects the service neutral to the grounding electrode system (ground rods, water pipe, etc.). This establishes a reference to earth.

Addressing Your Specific Questions
1. Can the Meter Can Act as a "Pass Through" for the EGC? Yes, technically, but with careful consideration. The NEC doesn't explicitly forbid this, but you need to ensure the meter enclosure is properly bonded to create a continuous, low-impedance path for fault current. Here's how: Adequate Size EGC

You must run an EGC sized according to NEC 250.122 based on the size of the feeder conductors (your parallel 250 kcmil AL conductors). This EGC must be continuous from the 800A disconnect to the 400A disconnect. This is what's critical.

Proper Connection

The EGC must be terminated properly at both the 800A disconnect (at the equipment grounding bus) and the 400A disconnect (also at the equipment grounding bus).


Bonding Locknuts

As you suggested, using bonding locknuts or grounding bushings on both ends of the nipple(s) connecting the 800A disconnect to the meter can, and the meter can to the 400A disconnect, is essential. This ensures the metal enclosures are properly bonded together, facilitating the fault current path.

Best Practice (Recommended)

While passing the EGC
through is permissible, it's often considered best practice to splice the EGC in a junction box within the meter enclosure. This allows for better inspection and ensures a solid, reliable connection. Use appropriate connectors listed for grounding and bonding. This provides a better mechanically secure and electrically sound connection for the EGC.2.

Power Company's GEC at the Meter Can
This is common and usually dictated by the utility. Bonding to Neutral

Yes, you typically bond the GEC to the neutral in the meter can (assuming it's a service-rated meter enclosure and the utility allows it). This creates the required connection to ground at the service.

Important Considerations and Recommendations
EGC Sizing

Based on 250 kcmil AL conductors, you need to size the EGC according to Table 250.122 of the NEC. For parallel conductors, you multiply the conductor size by the number of parallel runs when determining the EGC size. So with two parallel 250 kcmil AL conductors per phase, you would treat it like 500 kcmil AL. Therefore, you'll likely need a

1/0 AWG Copper
EGC per set of parallel conductors (or equivalent Aluminum if permitted). Double-check this with Table 250.122! Do the math. You must use the correct size. If you run (1) EGC for both sets of 250kcmil, then you must size the EGC per table 250.122 based off the 800 amp overcurrent device. Material Compatibility

Ensure all connectors are compatible with both aluminum and copper conductors, to avoid corrosion.


Torque

Torque all connections to the manufacturer's specifications. Loose connections are a major cause of electrical failures.

Inspection

This installation
will be inspected. Make sure everything is done according to the NEC and local amendments.

Grounding Electrode System

Make sure your grounding electrode system (ground rods, water pipe, etc.) is adequate and installed according to NEC 250.50 and following sections.

Clear Identification

Clearly label all conductors, especially the EGC and neutral.

In Summary

You must run a properly sized EGC from the 800A disconnect to the 400A disconnect. You can pass this EGC through the meter can, provided the meter can is properly bonded to the raceway system using bonding locknuts or grounding bushings. Consider splicing the EGC in a junction box within the meter can for better reliability and inspection. Follow the power company's requirements for the GEC at the meter can. Pay close attention to conductor sizing, material compatibility, and proper torqueing of connections.

Disclaimer:
I am an AI chatbot and cannot provide definitive electrical design advice. This information is for general guidance only. Always consult with a qualified and licensed electrician for your specific project and local codes. Flag for review