User: elohr46, Location: square one
Asked on: Thursday, December 23, 2010 at 10:23 am EST
Answered on: Monday, May 13, 2024 at 11:30 pm EDT
Question: Trying to get a clear understanding of 690.47(D) ex. #2. 2008NEC Situation; roof mounted solar array on a commercial one story building, building steel and steel bar joist is the grounding electrode system, is "on the roof" considered to be within 6' of the premises wiring electrode? We were going to run a GEC from the array down to building steel but not certain this is necessary, the metal conduit is being used as the equipment ground.
NEC 690.47(D)Exception No. 2: For roof-mounted equipment where the grounding electrode conductor(s) is (are) installed on the roof, the raceway or other equipment grounding conductor(s) used to interconnect the grounding electrode conductor(s) to the grounded PV system equipment can be reduced to a length of 6 ft (1.83 m) or less.
In this case: The solar array is roof-mounted. The building steel and steel bar joist is the grounding electrode system.* The metal conduit is used as the equipment grounding conductor.
Conclusion:Based on NEC 690.47(D) Exception No. 2, since the solar array is roof-mounted and the grounding electrode conductors are installed on the roof, it is not necessary to run a separate GEC from the array down to the building steel. The metal conduit used as the equipment grounding conductor can be used to interconnect the grounding electrode conductors to the grounded PV system equipment, provided its length is reduced to 6 ft or less.Therefore, the conduit can be used as the equipment ground without the need for a separate GEC. Flag for review