Topic: Time Clock with Aquatat

User: markstg, Location: Big Easy

Asked on: Friday, December 24, 2010 at 12:17 pm EST
Answered on: Monday, May 13, 2024 at 11:31 pm EDT

Question: I have a hot water recirculation pump (fractional HP, 120VAC) in a residence that is controlled by an aquastat. I want to put a Time Clock on it so it doesn't run late at night. In looking at the Intermatic ST01C, it seems from the instructions that the TC switch leg needs to be connected to the load all the time, and can't be interrupted by the aquastat contact. Is this correct?I was going to do the same for some photocell controlled lighting. If these won't work, guess I'm stuck with the more expensive Time Switches that have "real" contacts?Merry Christmas

Yes, that is correct. The Intermatic ST01C time clock requires the switch leg to be connected to the load all the time. This means that the aquastat contact cannot interrupt the power to the pump.You will need to use a time switch with "real" contacts for this application. These time switches have a separate set of contacts that are used to control the power to the load. The aquastat contact can then be used to open or close these contacts, turning the power to the pump on or off.Here is a wiring diagram for connecting a time switch with "real" contacts to a hot water recirculation pump:[Image of wiring diagram]In this diagram, the time switch is connected to the line voltage (120 VAC) and the load (the hot water recirculation pump). The aquastat contact is connected to the terminals on the time switch that are marked "Normally Open" and "Normally Closed".When the aquastat contact is closed, the power to the pump will be turned on. When the aquastat contact is open, the power to the pump will be turned off.You can also use a time switch with "real" contacts to control photocell controlled lighting. The wiring diagram for this application is similar to the one shown above.Merry Christmas to you too! Flag for review

Previous Question Next Question