User: Trowbridge - Martin, Location: Chapel Hill, NC
Asked on: Friday, December 24, 2010 at 4:14 pm EST
Answered on: Monday, May 13, 2024 at 11:32 pm EDT
Question: New galvanized gas piping is installed for one new gas range in existing single family home. Florida Building Code Residential Fuel gas states:CHAPTER 24 RESIDENTIAL FUEL GASG2411.1 (310.1) Gas pipe <<bonding>>. Each above-ground portion of a gas piping system that is likely to become energized shall be electrically continuous and <<bonded>> to an effective ground-fault current path. Gas piping shall be considered to be <<bonded>> where it is connected to appliances that are connected to the equipment grounding conductor of the circuit supplying that appliance.It appears that no external bonding is necessary to the pipe from: service equip enclosure, the grounded conductor at the service, the grounding electrode conductor or to one or two of the grounding electrodes used.Second question - if copper water piping is bonded at tank can outside water pipe ever be used for gas pipe bond?Thank you, Tom
First Question
Based on the provided code excerpt, it appears that external bonding of the new galvanized gas piping is not explicitly required if the following conditions are met: The gas piping is connected to appliances that are grounded (e.g., gas range) The appliances are connected to the equipment grounding conductor of the circuit supplying themTherefore, if the new gas pipe is properly connected to the gas range and the range is grounded, no additional external bonding is necessary.
Second Question
The Florida Building Code does not explicitly address using an outside water pipe as a bonding point for a gas pipe. However, the National Electrical Code (NEC) Article 250.120 (2020) states that:> "If the location of the grounding electrode that is used for the service is determined to be likely to be disconnected or is located so as to be unlikely to be accessible for the purpose of connecting the gas piping to it, the grounded neutral conductor at the service shall be used. . . ."This suggests that if the grounding electrode used for the service is not accessible or unlikely to remain connected, the grounded neutral conductor at the service should be used as the bonding point.
Conclusion: For the first question, external bonding of the galvanized gas piping is not required if the conditions outlined in G2411.1 (310.1) are met. For the second question, the code does not explicitly address using an outside water pipe for gas pipe bonding. However, if the grounding electrode used for the service is not accessible or unlikely to remain connected, the grounded neutral conductor at the service should be used as the bonding point. Flag for review