Topic: Pool Bonding

User: eds, Location: VA

Asked on: Friday, December 24, 2010 at 5:03 pm EST
Answered on: Monday, May 13, 2024 at 11:32 pm EDT

Question: I have a upcoming pool projects and would like to make sure my bonding confirms to the 08 code. Walls and floor of the pool are a sprayed on concrete, rebar is set and tied together, using a listed clamp a piece of #8 copper is clamped to rebar and brought to the deck area. All forming shells will have a #8 from lug to individual listed clamps on the rebar in the walls of the pool. Pool deck will be a concrete pour, stubbed out piece of #8 lands on one piece of rebar in the deck, all rebar is tied together with tie wire. At various locations bonding jumpers will be brought to handrail clamps, diving board bolts, ladder, and basket ball clamps, additionaly one piece of # 8 will be taken to the pool equipment room for equipment bonding. Will I also need to encircle the pool perimeter with a #8 clamped in 4 places, since the pool deck contains rebar?

Yes, you will also need to encircle the pool perimeter with a #8 wire clamped in 4 places.

According to the 2008 National Electrical Code (NEC), Article 680.26, all pools, spas, and hot tubs must have a bonding grid encircling the perimeter of the pool. This bonding grid must be made of solid copper or copper-clad steel wire, and it must be at least #8 AWG. The bonding grid must be connected to the rebar in the pool walls and floor, as well as to all metal components that are within 5 feet of the pool, such as ladders, handrails, and diving boards.The purpose of the bonding grid is to provide a low-impedance path for fault current to flow back to the electrical panel. This helps to protect swimmers from electrical shock if a fault occurs in the pool equipment.In your case, you have already provided bonding for the rebar in the pool walls and floor, as well as for the metal components within 5 feet of the pool. However, you have not yet provided a bonding grid around the pool perimeter. To ensure that your pool meets the requirements of the NEC, you will need to add a #8 wire bonding grid around the perimeter of the pool. Flag for review

Previous Question Next Question