Question: Hello:The National Electric Code requires the branch circuit to use no more than 80% of the circuit breaker (and wiring) rating for continuous loads. A continuous load is considered to be 3 hours (section 100 of NEC).My question: is it against the code if the circuit breaker runs at 125% rated current or so for a short period of time (e.g. several minutes)?Xing Fu
It is against the code if the circuit breaker runs at 125% rated current or so for a short period of time (e.g. several minutes).The National Electrical Code (NEC) requires that branch circuits be protected by circuit breakers or fuses that are rated for no more than 80% of the circuit's ampacity. This is to prevent the circuit from overheating and starting a fire.If a circuit breaker is running at 125% of its rated current, it means that the circuit is drawing more current than it is designed to handle. This can cause the circuit breaker to trip or the wiring to overheat.There are some exceptions to this rule. For example, motors are allowed to draw up to 125% of their rated current for a short period of time (e.g. several minutes). However, this is only allowed if the motor is properly sized and protected by a motor starter.If you are unsure whether or not your circuit is overloaded, it is best to consult with a qualified electrician. Flag for review