Topic: Cadwelding GEC

User: knoppdude, Location: Sacramento,ca

Asked on: Saturday, December 25, 2010 at 11:13 am EST
Answered on: Monday, May 13, 2024 at 11:32 pm EDT

Question: Does Cadwelding a grounding electrode conductor violate the code rule that the conductor must be continuous with no splices? I don' have the NEC handy 2008 edition, but if have seen this done to lengthen, and add connections to other grounding electrodes. Thanks for any and all responses.

Answer

No, welding does not violate this rule.

Explanation:
Section 250.64(C)(1) of the NEC 2008 allows splices only at accessible points. A Cadweld is considered a bolted connection and is therefore permitted. Flag for review