Question: We are being asked to install a new 480 volt 3 phase 3 wire 600 amp copper feeder to a distribution board at a machine shop to replace an existing aluminum feeder that was damaged by a forklift. Our plan was to run 2 parallel runs of 300MCM THHN copper wire in (2) 3" EMT Conduits, approximately 150 feet in length, with one # 1 CU ground wire in each conduit. The existing 600 amp feeder circuit breaker is 80% rated and the terminations are rated for 75 Deg C. The ambient temperature in the shop is less than 40 Deg C. The maximum calculated full load current draw of all of the loads present on the existing the distribution board is 430 Amperes. Is 2 sets of 300MCM Copper wire feeders an acceptable installation?
NEC Compliance
NEC 310.15(B)(16)
For 3-wire, 600-volt feeders, the minimum conductor size is 250 kcmil copper or 350 kcmil aluminum.
Load Carrying Capacity
NEC 310.15(C)(1)
For 300 MCM THHN copper wire in conduit, the ampacity is 310 amperes per conductor at 75°C.
Conduit Fill
NEC 310.15(B)(3)(a)
For two 300 MCM THHN copper conductors in a 3-inch EMT conduit, the fill is 62%. This is within the allowable 40% limit.
Grounding
NEC 250.122
For a 600-amp service, the required grounding electrode conductor size is #1 AWG copper.
Based on the above
2 sets of 300 MCM copper wire feeders are
NEC compliant for a 480-volt, 600-amp, 3-phase, 3-wire feeder. The ampacity of the 300 MCM copper conductors (2 x 310 amperes) exceeds the maximum calculated load current draw of 430 amperes. The 3-inch EMT conduits provide adequate space for the conductors. The #1 AWG copper ground wire in each conduit provides proper grounding.
Additional Considerations: Ensure that the terminations are rated for the appropriate conductor temperature (75°C). Verify that the ambient temperature is less than 40°C as specified.* Consider using Type XHHW or THWN-2 wire for improved heat resistance if ambient temperatures may exceed 40°C. Flag for review