Topic: voltage drop clarification
User: ocoee, Location: Golden Co
Asked on: Saturday, December 25, 2010 at 2:18 pm EST
Answered on: Monday, May 13, 2024 at 11:32 pm EDT
Question: Can someone please verify that I am doing this correctly. I am connecting 21 solar inverters to a 3 phase 4 wire 277/480 VAC panel. These inverters have a single pole 277 V output. 3 phases 7 inverters per phase 500 feet back to main service.Assuming max/output "load" of 177 amps per phaseHere is the voltage drop formula that I am usingVD= 1.73 . 12.9 . I . L/CMmy inputs are1. 1.732. 12.9 "approx" K value for copper3. 177 amps max output I4 500 feet distance back to service5 CM = 300,000 300mcmMy results are this VD= 6.58 V or 2.3% vdThe engineer I am working with on this project comes out with a wire size that is 600 MCM to achieve the same VD and his methods are cryptic at least to me.Please someone tell me that I have no idea what I am doing or confirm this is an acceptable resultthanks
Your calculations appear to be generally correct. Here's a breakdown of the formula you used and your inputs
Formula:
VD = 1.73 12.9 I L / CM
Inputs
1.73
This is a constant that represents the square root of 3, which is used to account for the three-phase system.
12.9
This is the approximate K value for copper, which represents the resistance per 1000 feet of conductor.
177
This is the maximum output current per phase.
500
This is the distance from the inverters to the main service in feet.
CM
This is the circular mils (CM) of the conductor.
Your Calculations
Using these inputs, your calculations for the voltage drop (VD) are as follows:VD = 1.73 12.9 177 500 / 300000VD = 6.58 V
This result indicates that you would experience a voltage drop of 6.58 volts, or approximately 2.3% of the nominal voltage (277 V).
Engineer's Calculations
Without knowing the specific methods used by the engineer, it's difficult to determine why they came up with a different wire size. However, it's possible that they considered additional factors such as:
Safety margin
They may have added a safety margin to account for potential variations in load and other factors.
Future expansion
They may have sized the wire to accommodate potential future expansion of the solar array.
Specific industry standards or guidelines
They may have followed specific standards or guidelines that require a larger wire size for a given voltage drop.
Acceptability of Results
A voltage drop of 2.3% is generally considered acceptable for most electrical applications. The National Electrical Code (NEC) allows for a voltage drop of up to 5% for branch circuits. However, lower voltage drops are always preferred, as they reduce power losses and improve system efficiency.
Conclusion:Based on the information provided, your calculations appear to be reasonable, and a voltage drop of 2.3% is generally acceptable. However, it's always advisable to consult with a qualified electrician to verify the design and ensure that it meets all applicable codes and standards.