Mike Dolt Enterprises Logo Mike Dolt Enterprises

Topic: voltage drop clarification

User: ocoee, Location: Golden Co

Asked on: Sunday, December 26, 2010 at 11:36 am EST
Answered on: Monday, May 13, 2024 at 11:33 pm EDT

Question: I am posting again to see who may reply, I posted yesterday It seems by the time several people chime in ( thank you) the original question gets lost or watered down.Here the input for my voltage drop Calc.1. 277/480V 3P 4W2. K value 12.9 for CU3. distance is 500' from sub panel to service( underground in PVC)4 load at the end of the circuit is 177 amps per phase5. wire selected 300MCMHere is my math VD= 1.73 . 12.9 . 177 . 500/300,000VD=6.58 or 2.3% line to NVD=6.58 or 1.3% line to lineQuestion 1 is this valid?Question 2 is the method the project engineer uses (below) more accurate?How he does it. Thank you all for your input! Happy holidays!1. Using the voltage and current and the formula R = V / I, calculate the resistance in your circuit that would result in 100% VD.2. Determine what voltage drop is acceptable as a percentage and multiply the value from Step 1 by that number. For example 2% would be 0.02 x R = Total Allowable Circuit Resistance3. In order to get to the ohms/1000ft given in Table 8 of Chapter 9 in the NEC, we then need to figure out how many 1000 ft sections we have in our circuit. If, as in this situation, we?re estimating the distance to be 500 ft from line to load, the math is easy. Our circuit is 500 ft out the line and 500 ft back along the neutral. That?s one 1000 ft section. Had it been 250 ft we?d be at only half of a 1000 ft section and so the resistance in the wire could be twice as much and have the circuit resistance stay the same.4. Then all that?s left is do divide the number from Step 2 by the number from Step 3 and compare it to the NEC.In our case then,R Total = 277 / 175 = 1.583 ohmsR Allowable = 1.5% * 1.583 = 0.0237 ohmsD = 530 * 2 = 1060 ft.L = D / 1000 = 1.06 thousand ftConductor Resistance = 0.0237 / 1.06 = 0.0224 ohms/1000ftLooking at Table 8, we then see that we need a wire of 600 MCM.Digging a bit deeper, Table 8 is really for DC. The AC table is Table 9, but it?s for uncoated conductors only. Looking at the impact coating has on DC conductors of this size, there appears to be about a 4.2% kicker. If we can translate that over to the AC table, it looks like our 600 MCM coated becomes 0.02397 ohms/1000 ft and is therefore too high for our needs. We?d either need to go to a 700 MCM or allow the higher voltage drop (1.61% by my calculations).Please either find fault in my calculation or provide your own to this detail. I?m afraid I still can?t determine where your numbers are coming from.

Question 1: Validity of Your Calculations

Your calculations appear to be valid and follow the correct formula for voltage drop:VD = 1.73 K I D / AWGHowever, there are some minor discrepancies in your values: You calculated a line-to-neutral voltage drop of 2.3%. However, the voltage drop should be 1.15% line-to-neutral given a 277V system. You calculated a line-to-line voltage drop of 1.3%. However, the voltage drop should be 0.69% line-to-line.

Question 2: Comparison with Project Engineer's Method

The project engineer's method is also valid and has some advantages over yours:
It is more precise as it considers the actual distance of the circuit, not just the round-trip distance from the panel to the load. It can be used with AC or DC circuits. It takes into account the impact of conductor coating on resistance.

Comparison of Results

Using the project engineer's method and assuming a 500ft distance (1000ft round-trip), the allowable circuit resistance is 0.0237 ohms.Using Table 8 of NEC Chapter 9, this resistance corresponds to a 600MCM conductor for DC.However, as the project engineer noted, Table 8 is for uncoated conductors. Applying the 4.2% correction factor for coated conductors results in an allowable conductor resistance of 0.0248 ohms/1000ft.This resistance corresponds to a 700MCM conductor for AC, which is consistent with the project engineer's recommendation.

Conclusion

Both your method and the project engineer's method are valid for calculating voltage drop. The project engineer's method is more precise, especially for circuits with non-uniform distances or conductor coating.In this case, your method slightly underestimated the voltage drop, while the project engineer's method gave a more accurate result. Flag for review

Previous Question Next Question