User: yetiman, Location: Raeford, NC
Asked on: Sunday, December 26, 2010 at 1:37 pm EST
Answered on: Monday, May 13, 2024 at 11:33 pm EDT
Question: I have a old existing 240v 3 wire uf feeder to a pump house that is about 3 feet from a natural pond. The customer wants to add a 240v 20a outlet on the outside of the pumphouse to feed a new aerator. The aerator would be on a 24hr timer inside the pumphouse. The way I interpret 682 is that only equip. installed outside would require an equipotential plane. If all the equip. were inside except the receptacle the pump would plug into then an equipotential plane is not required. Then the only req. would be a GFI breaker for the pump?The other rabbit snare is that now we would be changing the panel for the pumphouse and the pumphouse is right next to the pond. This new panel will be wired to service only line to line loads. According to 682.11 it needs to be 5' from the shoreline, do you think that means the building or the actual equipment inside? To me it may be a AHJ call seeing as it is an existing building. Any comments?
Equipotential Plane
The NEC does not require an equipotential plane for equipment installed inside a building, even if the building is near a body of water. However, if the receptacle that the aerator will plug into is installed outside of the pumphouse, then an equipotential plane would be required.
GFCI Breaker
A GFCI breaker is required for the outlet that the aerator will plug into, regardless of whether the outlet is installed inside or outside of the pumphouse.
Panel Location
The NEC requires that service equipment be located at least 5 feet from the shoreline of a body of water. This requirement applies to both the building that houses the service equipment and the service equipment itself. In this case, the pumphouse is considered to be the building that houses the service equipment. Therefore, the new panel must be located at least 5 feet from the shoreline of the pond, regardless of whether the equipment inside the panel is line-to-line or line-to-neutral loads.
AHJ Call
It is always advisable to consult with the local AHJ before making any changes to an existing electrical installation. The AHJ may have specific requirements or interpretations of the NEC that must be followed. Flag for review