User: dennisdamenace, Location: Tennessee
Asked on: Sunday, December 26, 2010 at 2:57 pm EST
Answered on: Monday, May 13, 2024 at 11:33 pm EDT
Question: I am trying to figure what I need to supply a peice of equipment for 2500 amps. I need to know what size wire and conduits I need. It will be 480 volt 3 phase. Also what size transformer I will need and the size of wire and conduit to feed a 4000 amp switchboard. Been racking my brain on these. Thank you so much for your help.
Equipment for 2500 Amps (480 V, 3 Phase)Conductors
Wire Size
750 MCM THHN copper wire
Conduit Size
4 inches
Transformer
Transformer Size
2000 kVA transformer
Primary Voltage
12 kV or 13.8 kV (as per local grid voltage)
Secondary Voltage
480 V
Switchboard for 4000 AmpsConductors
Wire Size
1500 MCM THHN copper wire
Conduit Size
5 inches
Transformer (if required)
Depends on the primary voltage available and the required secondary voltage. For example, if the primary voltage is 12 kV and the secondary voltage is 480 V, a 3000 kVA transformer would be required.
Additional Notes: The equipment must be installed in accordance with the National Electrical Code (NEC) or local electrical codes. Overcurrent protection devices (e.g., circuit breakers, fuses) must be properly sized and installed. The entire electrical system, including the transformer, switchboard, and conductors, should be designed and installed by a qualified electrician. Ventilation and cooling requirements for the transformer and switchboard must be considered. Proper grounding and bonding practices must be followed. Flag for review