Mike Dolt Enterprises Logo Mike Dolt Enterprises

Topic: Outside taps, NEC 2008 p87 240.21 (B) (5)

User: AK D, Location: New Jersey

Asked on: Monday, December 27, 2010 at 5:23 pm EST
Answered on: Monday, May 13, 2024 at 11:33 pm EDT

Question: Does this mean we can run a tap beyond 10', even all the way around the outside of a house, if need be? We would just need to be sure the conductors terminate in a single breaker, in contrast to within 10', where we can terminate in a main lug panel.Am I correct in my interpretation?

Yes, you can run a tap beyond 10', even all the way around the outside of a house, if need be. The National Electrical Code (NEC) allows this provided that the conductors terminate in a single breaker and the tap conductors are not more than 6 feet in length. This is in contrast to a tap within 10', which can terminate in a main lug panel.This means that you can use a tap to connect a remote building or structure to your main electrical service, even if the distance is greater than 10'. However, you must be sure to follow the NEC requirements for tap conductors, including the following: The tap conductors must be sized according to the load they will be carrying. The tap conductors must be installed in a conduit or other approved raceway.* The tap conductors must be protected by a circuit breaker or fuse.By following these requirements, you can safely run a tap beyond 10' to provide power to your remote building or structure. Flag for review

Previous Question Next Question