Mike Dolt Enterprises Logo Mike Dolt Enterprises

Topic: Metal Enclosures

User: al, Location: Minnesota

Asked on: Monday, December 27, 2010 at 6:46 pm EST
Answered on: Monday, May 13, 2024 at 11:34 pm EDT

Question: Is a cable tray considered a metal enclosure for grounding purposes?250.86:Exception No. 2: Short sections of metal enclosures orraceways used to provide support or protection of cableassemblies from physical damage shall not be required tobe connected to the equipment grounding conductor.I know that cable tray is not considered a receway. Is it a metal enclosure?

No, a cable tray is not considered a metal enclosure for grounding purposes.The term "metal enclosure" in the NEC refers to an enclosure that is designed to contain electrical equipment and protect it from physical damage. Cable trays are not designed for this purpose; they are designed to support and protect cables. Therefore, they do not meet the definition of a metal enclosure and are not required to be connected to the equipment grounding conductor. Flag for review

Previous Question Next Question