Question: When calculating the NEUTRAL in the Optional residential method- I revert to the Standard method to size the neutral.Do I reduce the '4 or more 120V fixed appliances' load by 75% ?My CE text book is excellent but does not reduce the Demand Factor for these when calculating the neutral.The Annex D examples in the NEC doesn't address this, too few fixed appliances.Article 220.53, and of course 220.61, both seem like they'd apply, to me.
Yes, you reduce the '4 or more 120V fixed appliances' load by 75% when calculating the neutral using the Optional Residential method.According to NEC Section 220.53, the demand factor for lighting and receptacle loads is 75% for loads over 16 kVA and 100% for loads 16 kVA and less.Section 220.61 specifies that the optional neutral can be sized using the standard method, where the neutral current is calculated as the maximum unbalanced load plus additional loads as specified in Section 220.61(B).Since the standard method is used to size the neutral, the demand factor for the 4 or more 120V fixed appliances should be reduced by 75% according to Section 220.