User: Maverick99, Location: Chapel Hill, NC
Asked on: Tuesday, December 28, 2010 at 9:15 am EST
Answered on: Monday, May 13, 2024 at 11:34 pm EDT
Question: I have a problem in that I have to add a meter and panel to a 240/480 single phase service. Quite an odball and I can't seem to find a supplier that can supply a NEMA 3, 480 Volt single phase panel. They can all supply a 3 phase panel.I have not been able to find anything in the codes that preclude me from using a 3 phase panel as single phase, but I am afraid that I am just missing it.Can anyone help me with this?Thanks
Code Compliance
There is no code violation in using a three-phase panel as a single-phase panel.
National Electrical Code (NEC) Section 408.3(B) states, "Where single-phase loads are connected between phases of a polyphase system, the branch-circuit or feeder conductors shall have an ampacity not less than 100 percent of the load current." Section 408.3(C) states, "Where single-phase loads are connected to different phases of a polyphase system, the branch-circuit or feeder conductors shall have an ampacity not less than 50% of the load current."These code requirements are based on the principle that single-phase loads on a three-phase system draw current from only two of the phases. Therefore, the ampacity of the conductors must be sized appropriately.
Panel Considerations
When using a three-phase panel for single-phase service, it is important to consider the following:
Phase Configuration
The panel must be configured for single-phase, meaning that only one phase will be utilized.
Grounding
The grounding system must be compatible with the type of service being provided (240/480V single-phase).
Bus Rated for Single-Phase
The busbar system within the panel must be rated for single-phase currents.
Available Spaces
Ensure there are enough vacant breaker spaces for the required circuits.
Supplier Availability
While it may be difficult to find a supplier that specifically sells 480V single-phase panels, you can utilize a three-phase panel with the appropriate modifications. Many electrical supply houses and distributors can provide guidance and support in configuring the panel for single-phase use.
Additional Resources
Square D Technical Bulletin
https://www.se.com/ww/en/download/document/SSU-1009-01_Technical_Bulletin-Single-Phase-Loads-on-Three-Phase-Panelboards/
Hubbell Wiring Device-Kellems Technical Bulletin: https://www.hubbellchannel.com/resources/documents/issues/pdf/TB-0131_SinglePhaseLoadsThreePhasePanelboards.pdf Flag for review