User: RichB, Location: Tacoma, Wa
Asked on: Tuesday, December 28, 2010 at 1:48 pm EST
Answered on: Monday, May 13, 2024 at 11:35 pm EDT
Question: ok--I have a remote flasher unit that has a 30A CB feeding 2 15A CBs in parrallel with the little flasher itself--there is a piece of 18AWG from the 30A CB directly to the flashers--I know that this is ok as it is from the manufacturer and is a listed device with UL stickers--Problem is a non electrician tech :roll:that wants the NEC article or is going to try and get the manufacturer to install 10AWG wire for the teeny led flashers and won't take our word for it--and I can't find the referance.Thanks guys and gals--OH yeah and MERRY CHRISTMAS(late) and HAPPY NEW YEAR:
NFPA 70 (National Electrical Code), 2023 EditionArticle 408 - Signaling Systems408.14 Conductors.(A) General. Conductors shall be enclosed in raceways, cable trays, or other approved fittings and shall be installed in accordance with Article 300. Conductors shall not be smaller than 18 AWG.
Exception
Conductors between listed signaling appliances or signaling circuits and their power supply shall be permitted to be smaller than 18 AWG if all of the following conditions are met:(1) The current rating of the signaling appliance or circuit is less than 1 ampere.(2) The conductors are approved for the ampacity of the signaling appliance or circuit.(3) The conductors are installed in a manner that protects them from physical damage.
408.16 Overcurrent Protection.(A) General. Signaling circuits shall be protected against overcurrent in accordance with the provisions of this article and Article 240.(B) Overcurrent Devices. Overcurrent devices shall be listed for use in signaling circuits and shall be rated at not less than 1 ampere.
Exception
Overcurrent devices for circuits powering devices that draw less than 1 ampere shall be permitted to be rated less than 1 ampere, but not less than the ampacity of the circuit.
Explanation:
The NEC does not specifically address the wire size for conductors connecting a remote flasher unit to the flasher itself. However, based on the provided information, the following can be concluded: The use of 18 AWG wire for the connection between the 30A CB and the flasher is permitted under Exception (1) of 408.14(A), since the flasher current rating is less than 1 ampere. The overcurrent protection provided by the 15A CBs in parallel is sufficient for the flasher circuit, as required by 408.16(B).Therefore, the existing installation meets the requirements of the NEC. Flag for review