Mike Dolt Enterprises Logo Mike Dolt Enterprises

Topic: Calculate current limiting effect of conductor length..

User: richwaskowitz, Location: Shelby Twp. MI, near Detroit

Asked on: Tuesday, December 28, 2010 at 2:43 pm EST
Answered on: Monday, May 13, 2024 at 11:35 pm EDT

Question: 1. An industrial control panel is labeled with an SCCR of 5kA2. The feeder supplying it utilizes a J class 25 amp fuse with a let-through current of 5.5kA (UL 508A table SB4.2)3. I want to prove that a 50 foot length of #10 cable supplying power to this 5 kA rated panel will effectively limit the available fault current to a value below 5kA.Can it be as simple as taking the resistance of 50 feet of #10 at 0.05 ohms times 2 (out and back) for a total of 0.10 ohms, using I=E/R and coming up with 480 V / 0.1 Ohms = 4800 Amps?

Yes, your approach is correct and can be used to prove that the 50-foot length of #10 cable will effectively limit the available fault current to a value below 5kA.

Here are the steps:1. Calculate the resistance of the 50-foot length of #10 cable:

R = 2 x (50 ft x 0.05 ohms/ft) = 5 ohms
`2. Use Ohm's law to calculate the available fault current:
I = E/R = 480 V / 5 ohms = 96 Amps
This value is below the 5kA SCCR rating of the industrial control panel. Therefore, the 50-foot length of #10 cable will effectively limit the available fault current to a value below 5kA. Flag for review

Previous Question Next Question