Question: I inherited a machine which has five motor starters all bussed togethere across the top of the OL unit. Originally the five motors were .75, 1.5, 2, 2, and 3 horsepower and the fuse feeding all five starters was specified to be 30 amps. I have replaced the 3 hp motor with a 10 hp including the proper OL unit and contactor. I am unsure of how to properly size the fuse now. Do I size the fuses by figuring the total horsepower? If that's the case, 30 amps seems appropriate given the total hp before I made the changes.Voltage is 480 FWIW.Thanks in advance.
Calculating Fuse Size
To determine the appropriate fuse size, you need to calculate the total current draw of the five motors. Step 1: Convert horsepower to full-load amps (FLA) 0.75 hp = 3.5 amps 1.5 hp = 7 amps 2 hp = 9.5 amps 2 hp = 9.5 amps 10 hp = 21 amps Step 2: Calculate total FLA FLA = 3.5 + 7 + 9.5 + 9.5 + 21 = 50.5 ampsFuse Selection
Based on the total FLA of 50.5 amps, you need to select a fuse that is rated for the next standard size above this value. This is typically a 60-amp fuse.
Reasoning for Sizing Increase
The original fuse size of 30 amps was likely sufficient for the original motor configuration because the motors were smaller and drew less current. However, the addition of a 10 hp motor significantly increases the overall current draw.
Using Total Horsepower
While the total horsepower of the motors can provide a general estimate of the current draw, it is not an accurate way to size the fuse. The actual current draw depends on the FLA of each motor, which can vary depending on factors such as efficiency and operating conditions.Therefore, it is recommended to calculate the total FLA and select a fuse based on that value, taking into account any potential future changes or additions to the motor configuration. Flag for review