User: Saywatt, Location: Chapel Hill, NC
Asked on: Tuesday, December 28, 2010 at 6:54 pm EST
Answered on: Monday, May 13, 2024 at 11:36 pm EDT
Question: Home inspector sited that the gas pipe (1" galvanized) that feeds a 60kva generator be bonded for lightning protection.The generator is controlled by a ats that does not open the neutral.This is a 400-amp service and the gas meter (not bonded) is on the opposite side of the house.Since the ats does not open the neutral, wouldn't the feeder ecg be a sufficient bond, or does it need to be bonded to the service gec?
The home inspector is correct in stating that the gas pipe that feeds the 60kva generator should be bonded for lightning protection. This is because the gas pipe can provide a path for lightning to enter the home and cause damage.The electrical code requires that all metal piping that enters a building be bonded to the electrical service ground. This includes gas pipes, water pipes, and drain pipes. The purpose of this bonding is to ensure that there is a low-resistance path for lightning to follow so that it does not enter the home and cause damage.In this case, the gas pipe that feeds the generator is not bonded to the electrical service ground. This is because the ATS does not open the neutral. As a result, there is no path for lightning to follow to the electrical service ground.To correct this problem, the gas pipe should be bonded to the electrical service ground. This can be done by installing a bonding jumper between the gas pipe and the electrical service ground. The bonding jumper should be made of copper wire that is at least #6 AWG.Once the gas pipe is bonded to the electrical service ground, lightning will be able to follow a low-resistance path to the ground. This will help to protect the home from damage. Flag for review