User: gk351, Location: IL
Asked on: Tuesday, December 28, 2010 at 9:33 pm EST
Answered on: Monday, May 13, 2024 at 11:36 pm EDT
Question: Currently have a 400 Amp service that feeds multiple motors plus a small lighting load. The user is adding another 50Hp and 20Hp motor (240 3ph) and I already know that the current 400 Amp won't cut it. I'm thinking of going with a 600A service due to limitations from the POCO. So I want to accurately calculate what the true load is going to be. This is for a fertilzer dealership, and they probably have in excess of 25 motors total!! Just need some advice on accurately doing a load calc! Thanks!
Step 1: Gather Motor Data
Collect the following information for each motor: Motor nameplate data (horsepower, voltage, phase, full-load amps (FLA)) Operating hours per day Duty cycle (percentage of time motor is running)Step 2: Calculate Motor KVA
For each motor, calculate the motor's KVA (kilovolt-amperes) using the formula:
Step 3: Calculate Load DemandMotor KVA = FLA x Voltage x 1.73 x √3
Sum the KVA values of all the motors to determine the total load demand:
Step 4: Apply Diversity FactorTotal Load Demand = Σ (Motor KVA)
Since not all motors will operate simultaneously, apply a diversity factor to the total load demand to account for this. For a fertilizer dealership with a large number of motors, a diversity factor of 0.85 is reasonable.
Step 5: Calculate New Service AmperageAdjusted Load Demand = Total Load Demand x Diversity Factor
Determine the new service amperage required to meet the adjusted load demand:
Example CalculationNew Service Amps = Adjusted Load Demand / Voltage
Assuming you have the following motors: 50Hp motor (240V, 3ph, 120 FLA) 20Hp motor (240V, 3ph, 48 FLA) 25 additional motors with an average FLA of 20 amps
Step 1
Gather Motor Data 50Hp motor:FLA = 120 amps 20Hp motor:FLA = 48 amps Average FLA for additional motors:20 amps
Step 2
Calculate Motor KVA 50Hp motor: 120 x 240 x 1.73 x √3 = 31.23 KVA 20Hp motor: 48 x 240 x 1.73 x √3 = 12.48 KVA Additional motors: 25 x 20 x 240 x 1.73 x √3 = 166.56 KVA
Step 3
Calculate Load Demand Total Load Demand = 31.23 KVA + 12.48 KVA + 166.56 KVA = 210.27 KVA
Step 4
Apply Diversity Factor Adjusted Load Demand = 210.27 KVA x 0.85 = 178.73 KVA
Step 5
Calculate New Service Amperage New Service Amps = 178.73 KVA / 240V = 744.7 ampsTherefore, a 600 Amp service would not be sufficient to meet the new load demand. You would need to upgrade to a service size of at least 800 Amps.
Additional Considerations: Consult with the local utility (POCO) regarding their specific requirements and limitations. Consider the future growth potential of the load. Allow for a margin of safety in your load calculations. Flag for review