User: vilasman, Location: Chapel Hill, NC
Asked on: Wednesday, December 29, 2010 at 6:20 pm EST
Answered on: Monday, May 13, 2024 at 11:37 pm EDT
Question: I did a job where I have to run wiring from a rooftop solar array to the main circuit breaker box. Went to inspection and the inspector flagged me for using THHN and not THWN-2, citing that because of the heat on the roof, the internal temperature in the EMT could cause a problem with the insulation on the wiring. I'll buy that. He referred me 310.16, the temperature correction factor chart. He also referred me 3.15B-2c which he said deals with outside wiring. I can't find this chart in my 2005 code book, which I believe they are still using here in Maryland.I have (12) 10 gauge + (1) 8 gauge (green) in 1" EMT with compression connectorsNow here's my central question. As I read 310.16 it states it's referring to 3 current conductors in per stick of EMT. Does this mean that I cant run more than 3 current carrying conductors per stick?
THHN vs. THWN-2
The inspector's objection to using THHN wire instead of THWN-2 wire is valid. THWN-2 wire has a higher temperature rating (90°C) than THHN wire (75°C), which makes it more suitable for use in high-temperature environments like rooftops.
Section 310.16
Section 310.16 of the NEC provides temperature correction factors for conductors in raceways. It does not limit the number of current-carrying conductors in a raceway to three. However, this section may be used to determine the ampacity of the conductors based on the temperature inside the raceway.
Section 3.15B-2c
The inspector likely meant to refer to Section 310.15(B)(2)(c), not 3.15B-2c. This section states that "conductors shall be installed in raceways, cable trays, or other approved means" and that "conductors in raceways shall be installed to prevent physical damage."Can You Run More Than Three Current-Carrying Conductors in EMT?
Yes, you can run more than three current-carrying conductors in EMT, provided that: The conductors are spaced properly (see Section 300.34) The ampacity of the conductors is adjusted based on the number of conductors and the temperature inside the raceway (see Section 310.16) The raceway is sized appropriately for the number of conductors (see Section 314.16) The raceway provides protection against physical damage (see Section 310.15(B)(2)(c))In Your Case
For your case, with 12 10 AWG conductors and 1 8 AWG conductor in a 1-inch EMT, you would need to calculate the ampacity of the conductors using Table 310.16 and adjust it based on the number of conductors and the temperature inside the raceway. You would also need to ensure that the EMT is sized appropriately and that the conductors are spaced and protected properly. Flag for review