User: bkelly, Location: Logan, Utah
Asked on: Thursday, December 30, 2010 at 9:41 am EST
Answered on: Monday, May 13, 2024 at 11:38 pm EDT
Question: I know this has been hashed and re-hashed, but still can't seem to find an answer. I have a large 3 story single apartment building. It has a pad mount transformer, 2 underground laterals, one feeding a 2000a main on exterior for 72 meter packs. The other lateral feeds a 1200a MDP inside the building for all "house power". This seems to violate 230.72, "Grouping of Disconnects". My concern in the event of a fire, the FD will only see the exterior main, and not the interior MDP. Any thoughts?P.S. Happy New Year everyone.
NEC 230.72 - Grouping of Disconnects
The intent of NEC 230.72 is to ensure that all disconnecting means for a building are conveniently located and readily accessible so that the supply can be quickly disconnected in the event of an emergency.
Interpretation of the Code
In the scenario described, the exterior 2000A main serves as the service disconnecting means for the meter packs, while the interior 1200A MDP serves as the distribution disconnecting means for the house power. While the exterior main is readily accessible, the interior MDP is not because it is located inside the building.
Code Compliance Concerns
The separation of the service disconnecting means and the distribution disconnecting means in this manner could be interpreted as a violation of NEC 230.72. In the event of a fire, firefighters could potentially miss the interior MDP, which could delay the disconnection of power and put occupants at risk.
Fire Department Communication
It is crucial to coordinate with the local fire department to ensure that they are aware of the building's electrical system and the location of all disconnecting means. Providing clear instructions to firefighters on how to access the interior MDP in an emergency would help mitigate the risk of an oversight.
Alternatives
To address the potential code violation, one could consider the following alternatives: Relocate the MDP
Move the MDP to an exterior location to make it readily accessible to firefighters.
Install a Secondary Disconnect
Install an additional disconnecting means near the exterior main that simultaneously disconnects the MDP.*
Provide Firefighter Access
Create a dedicated access point or provide clear signage to guide firefighters to the interior MDP.
Recommendation
Contact the local fire department to discuss the specific concerns and determine the best course of action to ensure compliance with NEC 230.72 and the safety of occupants in the event of an emergency. Flag for review