User: inspector 102, Location: Northern Indiana
Asked on: Thursday, December 30, 2010 at 11:14 am EST
Answered on: Monday, May 13, 2024 at 11:39 pm EDT
Question: The local fire department has a rescue vehicle with a PTO generator for their scene lighting. The lighting circuit is protected by a 2-pole 20 amp circuit with GFCI protection. The GFCI breaker appears to be worn out and needing replaced. Article 445 appears to be the applicable section, but when checking the index, it show to check Art. 445.20 for GFCI requirements. There is no 445.20 in my book. Is there a section where I need to look to determine if GFCi is actual required for the lighting circuit on this vehicle. The receptacles are twist locks and do do have GFCI protection on the circuit. Thanks for the guidance.
NFPA 70 (NEC) 2023Article 445.20 in the NEC 2023 refers to Ground-Fault Circuit-Interrupters (GFCIs) for personnel protection in general use. It states that GFCIs are required for personnel protection in the following locations: Bathrooms Garages Outdoor outlets Crawl spaces Wet or damp locations Other locations as specified in the CodeArticle 445 specifically addresses GFCI requirements for portable generators.
NEC 2023 Section 445.14(H) states the following:> "If the portable generator has an AC output greater than 150 volts to ground, it shall be protected by a ground-fault circuit-interrupter (GFCI) in addition to the grounding requirements in 445.12."Interpretation
Based on the information provided, the rescue vehicle's lighting circuit is protected by a 2-pole 20 amp circuit with GFCI protection. Since the output voltage of the PTO generator is likely to be greater than 150 volts to ground,
GFCI protection is required for the lighting circuit as per NEC 2023 Section 445.14(H).
Conclusion:
Yes, GFCI protection is required for the lighting circuit on the fire department's rescue vehicle. Flag for review