Question: We have a 1200 amp service with existing 3-4" PVC conduits from power company transformer to Main disconnect. We want to use 700 MCM XHHW-2 aluminum to feed the main. Is this acceptable. We realize that we are using the 90 degree rating of 420 amps for the aluminum. The terminal lugs are rated @ 90 degrees.
Using 700 MCM XHHW-2 aluminum to feed a 1200 amp main disconnect may not be acceptable due to the following reasons: Ampacity and Conduit Fill
The 90-degree ampacity rating of 420 amps for 700 MCM XHHW-2 aluminum is not sufficient to carry the full 1200 amp load. Even if you account for derating factors (e.g., temperature, number of conductors in conduit), it is unlikely that the wire will be able to handle the required current.
Conduit Fill
The size of the conduit (4 inches) is also not sufficient to accommodate the large number of 700 MCM wires required to carry 1200 amps. Using multiple conduits in parallel may be necessary, which would add complexity and cost to the installation.*
Terminal Lug Rating
While the terminal lugs may be rated for 90 degrees, it is important to ensure that the wire ampacity is compatible with the lug rating. Since the wire is derated due to bundling and temperature, it may not be able to fully utilize the 90-degree ampacity of the lugs.
Recommended Approach:
It is recommended to consult with an electrical engineer or the local electrical inspector to determine if the proposed wire size and conduit configuration are acceptable. They can provide a detailed analysis based on the specific conditions of the installation and ensure compliance with applicable codes and standards. Flag for review