Mike Dolt Enterprises Logo Mike Dolt Enterprises

Topic: Isolated Ground Options

User: ttrotter, Location: Macon, GA

Asked on: Thursday, December 30, 2010 at 3:59 pm EST
Answered on: Monday, May 13, 2024 at 11:39 pm EDT

Question: OK, not sure if I have ever actually posted anything here or not?been a fan for years. I am an electrical engineer ? been doing this about 15 years. Feel free to take your shots.I have an isolated ground question?which I have read many, many threads about.The AV designer on a project I am working on in Georgia insists on IG receptacles for their equipment. The contractor installed the IG receptacles AND installed the separate IG and EG conductors from each IG receptacle back to the serving panelboard. That panelboard has a separate isolated ground bar onto which the IG conductors from these branch circuits were landed.Here is where it gets interesting. This branch circuit panelboard (100 amps, 208v, 3 phase) is served from a 600 amp, 208v, 3 phase distribution panelboard in another part of the building. The building service is 480/277 volts, 3 phase so this distribution panel is fed by a dry type transformer. The contractor did not include a separate IG conductor in with the feeder conductors from the distribution panel to the downstream branch panel. This feeder is installed in RMC and includes an insulated EGC. The feeder conductors are now installed and connected.I would normally take a separate insulated ground conductor all the way back to the dry type transformer XO bushing. It would route through and not be bonded to the distribution panel as allowed by the NEC. Since this was not done the way I see it the contractor has two options available (without physically pulling out the feeder conductors and pulling in a separate ground conductor) for this installation to comply with NEC:Option 1- Use the existing insulated equipment ground conductor installed with the feeder as an IG conductor. This would require installing an isolated ground bar in the distribution panelboard. The equipment grounding conductor installed with the feeder serving the downstream panel with IG loads would be terminated on this IG ground bar. The RMC would then become the equipment grounding conductor.Option 2 ? Just bond the isolated ground bar to the standard panelboard ground bar in the branch circuit panelboard. I realize this defeats the purpose of the IG ground bar?but I am not sold on the effectiveness of IG anyway. I can tell the AV guy that we have IG outlets and separate insulated grounding conductors, isolated from the metallic box/conduit system back to the serving panel. That much is true.Thoughts?

Regarding Isolated Ground (IG)

Isolated ground (IG) systems are designed to minimize noise and interference in sensitive electronic systems. They create a separate ground path that is isolated from the building's grounding system and electrical noise.

Options for IG Installation

In this case, since a separate IG conductor was not installed with the feeder from the distribution panel to the branch panel, you have two options

Option 1: Using the Feeder EGC as an IG Conductor
Install an isolated ground bar in the distribution panel. Terminate the EGC from the feeder on the isolated ground bar. The RMC conduit becomes the equipment grounding conductor (EGC).

Option 2: Bonding the IG Ground Bar to the Panelboard Ground Bar
Bond the isolated ground bar in the branch circuit panel to the standard ground bar.

Assessment of Options Option 1

This option maintains the separation of the IG system from the building's grounding system. However, it requires additional work to install the isolated ground bar in the distribution panel.


Option 2

This option defeats the purpose of the IG system by connecting it to the building's grounding system. However, it is simpler to implement and may still provide some noise reduction benefits.

Personal Opinion on IG


The effectiveness of IG systems can vary depending on the specific application and environment. Some engineers believe that IG systems can significantly reduce noise and interference, while others find that the benefits are minimal.

Recommendation

Based on the information provided, Option 1 is the more compliant and effective solution for this installation. It maintains the separation of the IG system from the building's grounding system and provides the intended noise reduction benefits.

Communication with the AV Designer

It is important to communicate your concerns and recommendations to the AV designer. Explain the options and their implications, and seek their input. If they insist on IG outlets but are not willing to implement a fully compliant system, you may need to document your concerns and proceed with the installation as directed. Flag for review

Previous Question Next Question