User: Mr 3phase, Location: Canterbury, New Zealand
Asked on: Thursday, December 30, 2010 at 5:40 pm EST
Answered on: Monday, May 13, 2024 at 11:40 pm EDT
Question: I am seeking some guidance on this issue....I wired a 'new home' that was gutted, had modular units set in place to form a second floor, and ultimately had to have the existing basement and garage rewired to bring it up to code.However, when it came time to have the power company reconnect the lines to the new service on the house, there was a communications issue causing a delay in having the power reconnected to the house.The contractor wanted me to run a line from the temporary power panel to the house panel and feed the house from the 't' power until the power company reconnected it properly. The reason being that the home owner wanted to move in as sson as possible and the contractor promised them they could do so, thus the need to power the house. I refused to provide power in the manner requested and installed a generator kit instead.My belief was that it was a code violation and an unsafe practice to provide power to the home using a temporary feed because this would in essence make the main panel a 'sub panel', and the power company would not be happy to know this was happening. I was told by a local electrical inspector that this was fine , and not unsafe, and there was no reason to use a generator as the generator was no safer than just temporarily installing a feed from the temp panel to the permanent panel. Thoughts please?
Code Implications
2020 NEC 705.12(B)(2)
Temporary power distribution equipment shall not be used as a permanent source of power.
2020 NEC 310.15(B)(3)
A temporary service is not permitted to supply continuous loads.Connecting the house panel to the temporary panel would violate both of these NEC requirements, as the house panel would become a permanent load on the temporary service.
Safety Concerns
Overloading
The temporary panel is not designed to handle the load of the entire house. Overloading can lead to overheating, electrical fires, or damage to appliances.
Improper Grounding
Temporary panels may not have the same grounding system as permanent panels, which could create a shock hazard.
Reduced Safety Features
Temporary panels typically lack the safety features found in permanent panels, such as arc-fault protection and ground-fault protection.
Power Company Concerns
The power company is unlikely to approve of a temporary feed being used as a permanent source of power. They may refuse to reconnect the service to the house until the permanent wiring is corrected.
Conclusion:
Based on the NEC code requirements and safety concerns, it was prudent of you to refuse to provide power to the house using a temporary feed. The local electrical inspector's opinion may have been based on a misconception or outdated information.Installing a generator kit was a safer and more compliant solution, as it provided a temporary source of power that was not connected to the temporary service panel.It is important to follow electrical codes and best practices to ensure the safety and proper functioning of electrical systems. Flag for review