Question: I have an electrical panel fed with four conductors (Black, Red, Blue, and White). I have 120V from any three of the hots to neutral, and I have 208V between any two of the three hots. My question is, can any 120V load whether it be receptacles, lighting, etc. be used with any of the three hots to neutral? Black/white, Red/white, or Blue/white. And, can all three hots (BLK, RED, BLUE) be ran with one shared neutral?Also, I have a machine going in that has as the spec rating, 30 amps 220 volts. I called the manufacturer and they said that 208 volt is fine for the machine which can operate on a voltage range of 208-240. Does this sound right?Thanks so much in advance.
120V Loads and Neutral
Yes, any 120V load can be used with any of the three hot wires (Black, Red, Blue) to neutral (White). It does not matter which combination of hot and neutral is used.
Shared Neutral
Yes, all three hot wires (Black, Red, Blue) can be connected to a single shared neutral wire.
220V Machine and Voltage:
Yes, it sounds right that the 30 amp 220 volt machine can operate on 208 volts. Most machines designed for 220 volts can tolerate a voltage range between 208 and 240 volts. However, it is important to verify the specific voltage range acceptable for your particular machine. Flag for review