User: Npstewart, Location: Massachusetts
Asked on: Thursday, December 30, 2010 at 10:17 pm EST
Answered on: Monday, May 13, 2024 at 11:40 pm EDT
Question: Had a discussion with a colleague of mine. We have a 1600A service, all the panels down stream are being fed from the MDP with (5) 400A/3P circuit breakers. I am saying we don't need a MCB because we can shut the building down with the five breakers which is less then six. He is saying we need a MCB because the sum of the breakers is greater than the total service size. (ie. (5) x 400A = 2000A) which is greater then 1600A.He is saying this is in the NEC. but I can't seem to find it anywhere. Ive been doing this a long time and never heard of this, has anyone else?If hes right, what would be the code section?Thanks GuysPS. The load calc for each respective panel is less then 400A, far less in most cases. The total demand is also less then 1600A.
Your colleague is mistaken. There is no requirement in the NEC to install a main circuit breaker (MCB) when the sum of the downstream circuit breakers exceeds the service size.The NEC only requires an MCB when the service is fed by a single circuit breaker or set of fuses. In your case, the service is fed by five circuit breakers, so an MCB is not required.In addition, your load calculations show that the demand on the service is less than 1600A, so even if an MCB were required, it would not need to be rated for 2000A.The code section that your colleague is likely referring to is NEC 240.85(5), which states:> "Where a building or structure is supplied by a single feeder, the feeder shall be protected by a single main circuit breaker or set of main fuses."However, this section does not apply to your situation because the service is not fed by a single feeder. Flag for review