User: Mr 3phase, Location: Massachusetts
Asked on: Friday, December 31, 2010 at 12:01 pm EST
Answered on: Monday, May 13, 2024 at 11:41 pm EDT
Question: I tried posting this before, but it did not show up.....I wired a home that was gutted, had a second floor added and basement redone. During this process the street service was removed from the home and installed on a temporary post, as a temporary service. When the new service was done on the house, there was a delay (turned out to be three weeks) before the power company reconnected the street lines to the house. In the mean time the owners wanted to move in as the house was done. The contractor wanted me to run a line from the 't power' to the house and feed the panel. I refused beleiving it was illegal, and provided a generator set up instead. The AHJ told me later that I could have done it, and it would be safe.Is there anything in the code that prohibits the use of 't power' to power a house panel? Looking for input.
National Electrical Code (NEC)Section 230.85 prohibits the use of temporary wiring for permanent installations, except for the following: Construction sites Exhibitions and displays Emergency situationsSection 230.95 specifically addresses temporary wiring for construction sites: It must be used only for temporary power during construction. It must be removed when permanent power is installed. It must meet all applicable NEC requirements, including grounding and bonding.
Exceptions
There are a few exceptions to the prohibition against using temporary wiring for permanent installations. One exception is when the temporary wiring is used to feed a
distribution panelboard during construction.
Section 230.95(C)(1) states that:> "Temporary wiring may be used to feed a distribution panelboard during construction of a dwelling unit or other structure where the installation complies with the provisions of Section 210.6."Section 210.6 requires that all service panelboards be located within the building they serve.
Conclusion
Based on the NEC, it is
not permitted to use "t power" to power a house panel permanently. However, it is permitted to use "t power" to feed a distribution panelboard during construction, provided that the installation complies with Sections 230.95(C)(1) and 210.
6.In your case, since the house was not under construction and the temporary service was intended to be permanent (until the street service was reconnected), it was not permissible to use "t power" to feed the house panel. Flag for review