Topic: Transfer switch requirements for residential standby generator

User: JosephPrince, Location: Toms River NJ

Asked on: Friday, December 31, 2010 at 5:00 pm EST
Answered on: Monday, May 13, 2024 at 11:41 pm EDT

Question: I have installed a Cutler Hammer 20 KW natural gas powered standby generator in a residential home. The home has a 200 amp overhead electrical service with the electric meter on the outside of the house, and a 200 amp main breaker electric panelboard directly below in a basement. My installation consists of: transferring the complete 200 amp panel with a 200amp rated automatic transfer switch located outside. I have taken the feeders off the load side of the meter enclosure and installed them to the utility side of the transfer switch. I then rerouted the conduit from the meter enclosure to the transfer switch and installed new feeders from the load side of the transfer switch to the existing panelboard. The transfer switch does not have a service disconnect, and to understanding of the code does not require one. Others are disagreeing and suggesting I need a t/s with a service disconnect. If this is correct, then I must now take all neutral and grounds in the main panel and separate them. What code article would I reference? What is your input to this installation.

NEC Requirements



225.30 (C)(1)

An automatic transfer switch shall serve only as a disconnect device when it is intended to be deenergized during maintenance or for inspection purposes.


225.30 (C)(2)

If the transfer switch is intended to be used as a service disconnect, it shall be marked "Suitable for Use as Service Equipment".

225.35 (A)(1) and (A)(2)

An exterior disconnecting switch or circuit breaker rated not less than 60 amperes shall be provided to each supply circuit inside the vicinity of the building where the circuit enters or leaves the building.

Installation Analysis

Based on the NEC requirements, the following points are relevant:


Transfer Switch Disconnect

Since your transfer switch does not have a service disconnect feature, it does not meet the requirements of 225.30(C)(2).

Exterior Disconnect

The installation does not include an exterior disconnecting switch or circuit breaker for the supply circuit entering the building. This is required by 225.35(A)(1).

Conclusion

The installation as described does not meet the NEC requirements for a standby generator system. You need to replace the transfer switch with one that is marked "Suitable for Use as Service Equipment" and has a service disconnect feature. You also need to install an exterior disconnecting switch or circuit breaker rated for at least 60 amperes.

Recommendation:


Consult with a qualified electrician to ensure the installation meets NEC requirements and ensures the safety of the home and its occupants. Flag for review