Mike Dolt Enterprises Logo Mike Dolt Enterprises

Topic: Single wire conductor insulation testing

User: solardoc, Location: Ohio

Asked on: Saturday, January 1, 2011 at 11:15 pm EST
Answered on: Monday, May 13, 2024 at 11:42 pm EDT

Question: I test for ground faults on a lot of single wire conductors that are run along metallic racking. When testing conductor insulation integrity, we normally isolate all condutors and test with a megger set at 1000V. We attach the red lead to the conductor and the black to the ground which is bonded to the racking. This test works well mot of the time, but sometimes the ground fault is caused by rain and by the time we are able to get to the site and test, the rain has dried up and the fault has cleared, all megger results are good. Will testing the conductor with one lead on the copper and one lead on the insulation show all damaged conductors? Is there another test that will reveal all compromised conductors?Thanks,Paul

Testing with Conductors and Insulation

Testing the conductor with one lead on the copper and the other lead on the insulation will only detect damage to the insulation. It will not reveal ground faults caused by contact between the conductor and the metallic racking.

Alternative Test: DC Hipot Test

A DC hipot test (also known as a dielectric withstand test or insulation breakdown test) is a more comprehensive test that can detect both insulation damage and ground faults. It involves applying a high voltage (typically 1000V or more) between the conductor and the ground for a certain period. If the insulation is damaged or there is a ground fault, the test will cause a breakdown and result in a high current flow.

Benefits of the DC Hipot Test

Can detect both insulation damage and ground faults Can be used on energized conductors (non-destructive test) Results are more reliable, as the test is not affected by moisture or temporary faults

Procedure for DC Hipot Test

1. Isolate the conductor under test from all other conductors and from the ground.
2. Connect the negative lead of the hipot tester to the conductor.3. Connect the positive lead of the hipot tester to the ground.
4. Apply the desired test voltage (typically 1000V or more).5. Observe the current flow for the duration of the test (typically 1 minute).
6. If the current flow is excessive (above a specified threshold), the conductor or ground fault is likely compromised.


Note:
DC hipot tests can be dangerous if not performed properly. Ensure that the tester is properly grounded and the area is clear of personnel.* The test voltage and duration may need to be adjusted depending on the insulation material and thickness. Flag for review

Previous Question Next Question