Topic: New GFCI Tripping

User: laketime, Location: Chapel Hill, NC

Asked on: Sunday, January 2, 2011 at 3:15 pm EST
Answered on: Monday, May 13, 2024 at 11:43 pm EDT

Question: I installed a dedicated circuit to a new GFCI on the exterior of a building. The customer wanted it to plug in block heaters for diesel equipment. The receptacle has been working fine for about 3 weeks. I got a call Friday saying that they now plug the equipment in (by extension cord) and the GFCI trips after about 30 minutes. I told them to check for damage on the cord. They said they had and everything was fine. What would you look for?

Potential Causes



Overheating

Diesel block heaters can draw high amps, potentially overheating the GFCI or wiring. Check for any signs of discoloration, burning, or melted insulation on the receptacle, wiring, or cord.


Moisture

GFCIs are sensitive to moisture. Check for any water ingress or condensation inside the receptacle box or along the cord. Ensure that the receptacle is weather-resistant and not exposed to rain or snow.

Ground fault

GFCIs are designed to detect and interrupt current imbalances caused by ground faults. Check for any cuts, nicks, or damage to the cord or wiring that could create a ground fault.


Faulty GFCI

Occasionally, GFCIs can malfunction or become damaged. Test the GFCI by pressing the "test" button. If it does not trip, the GFCI may need to be replaced.*

Extension cord issues

Extension cords can be a source of problems, especially when used with high-draw appliances. Check for any damage, loose connections, or overheating of the cord. Ensure that the cord is of adequate gauge for the amperage draw.

Troubleshooting Steps

1.

Inspect the cord and receptacle

Look for any visible damage, overheating, or moisture.2.

Test the GFCI

Press the "test" button on the GFCI to ensure it is functioning properly.3.

Try a different cord

If possible, try using a known-good extension cord or plug the equipment directly into the receptacle to eliminate the cord as the source of the problem.4.

Check amperage draw

Measure the amperage draw of the block heaters to ensure they are not exceeding the capacity of the circuit or GFCI.5.

Inspect the receptacle box

Make sure the receptacle box is weather-resistant and not exposed to moisture.6.

Replace the GFCI:
If all other troubleshooting steps fail, consider replacing the GFCI with a new one. Flag for review