Topic: tandem breakers in new panel installation

User: Ken 6789, Location: Tennessee

Asked on: Sunday, January 2, 2011 at 6:03 pm EST
Answered on: Monday, May 13, 2024 at 11:43 pm EDT

Question: Are tandem breakers ok to install in new panels. I only need to install one tandem. I can't find anything in the NEC prohibiting their use in new boxes nor in the local electrical code. I try to use tandems in existing boxes only. I'm assuming the AHJ cannot red flag me on this. Thanks

NEC Compliance

According to the National Electrical Code (NEC), tandem breakers are permitted in new panelboards. Section 408.16(A) states:> "Panelboards shall be designed and constructed so that no circuits or combinations of circuits are likely to be connected to the same phase conductor where the ampacity of the neutral conductor is based on the maximum unbalance among the phase conductors connected to the panelboard as determined by Section 220.
61."


Local Electrical Code

It is important to consult your local electrical code as it may differ from the NEC. However, it is unlikely that you will find any provisions prohibiting the use of tandem breakers in new panelboards.

Assumptions and Recommendations

While tandem breakers are generally permitted in new panels, it is not recommended to use them indiscriminately. Here are some factors to consider:

Minimize Use

Use tandem breakers only when necessary, as they can complicate troubleshooting and service.


Load Planning

Ensure that the connected loads do not exceed the ampacity of the tandem breakers and the panelboard.*

Wiring

Use properly sized wires and ensure that all connections are secure.

AHJ Approval

It is always a good practice to consult with your local Authority Having Jurisdiction (AHJ) to confirm their interpretation of the code. However, given the NEC and local code allowances, it is unlikely that the AHJ will red flag you for installing a single tandem breaker in a new panelboard.

Conclusion:


Based on the NEC and the information provided, it is generally acceptable to install tandem breakers in new panelboards as long as they are used sparingly and properly. Consult with your local AHJ to confirm their specific requirements. Flag for review